Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
 
Remember an RCD works by seeing an imbalance in the line and neutral current.All RCD's through which the supply passes will see an imbalance and trip.
Does beg the question as to why you have ditched a perfectly good TNCS for a rubbish TT though....although I've a feeling I'm going to deeply regret asking.
 
Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
why?...

you have stated 10mm SWA...is it a 3 core?

is there extranious in the shed?

or are you another of them that say you cant extend a PME?
 
Yup. Sounds like you are supplying DB2 from a RCD protected circuit on DB1. That will always happen.
it will happen if the top end RCD...(call it RCD 1) is being subjected to leakage from other circuits its offering additional protection to....also the individual device`s characteristics being taken into account.

smells like another poor design thread to me does this...
 
To be honest if it was stated somewhere that you could or shouldnt then i would or wouldn't!
Didnt want RCD in house to trip and cause nuissance to customer not that it should due yo the quality of the installation yoy understand?
I have been told over the years that outbuilidings cannot use PME?
More than happy if they can, saves me a lot of work.
 
DB1 RCD protecting 3 core SWA.
3rd core CPC not connected at DB2.
DB2 25/30m away.
so...whats the problem?

rite:

for a start get back round there and get that armoured off the RCD side of that board (top end).

get rid of that bloody rod in the shed.

use one of the cores (black) as the earth...take it straight into db2s MET.

use the grey as the neutral...get all cores identified top & bottom end (colours)

you have a 10mm CSA core in the SWA...so you dont need to be pulling in a seperate G/Y..do you (just before you bothered asking)...

30mA RCD in db2 for finals in there...
 
as glenn says. use 3rd core and armour ,earthed both ends, for cpc ( and bonding if required for extraneous). extend PME and forget the rod.
 
To be honest if it was stated somewhere that you could or shouldnt then i would or wouldn't!
Didnt want RCD in house to trip and cause nuissance to customer not that it should due yo the quality of the installation yoy understand?
I have been told over the years that outbuilidings cannot use PME?
More than happy if they can, saves me a lot of work.
well then you got told a load of old chud there didn`t you...
 

Reply to DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
892
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock