Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance "engineer" to commission Heat-Pump, as original company disappeared before installation. ASHP worked for a while then tripped the 100mA RCD not the 30mA. Both RCDs tested at nominal trip current and ramp test.....both passed. Selectivity obviously working fine. The supply works with a 3KW kettle and will operate with the ASHP if the earth is disconnected at the ASHP.
There is a very healthy earth to the DB.

Theories and similar experiences appreciated...........................
 
Sure thank you. LG R32 Monobloc.
What is the electrical power rating of the LG unit?

What is the make and model of type s rcd?

The research I have done does not turn up an RCD type. Indeed, LG literature is silent on any special requirements for type of rcd.

Could you sketch the intake, type S, dbs, final circuits etcetera for me to study please.

I would do some N to E insulation testing of the final circuits If you have not already.

Also, could you measure voltage between N ( at main switch) to E on earth bar with a voltmeter not AVT at no load, light load, medium load and full load? Want to see if N voltage wrt local earth rises by much as loading increases.. Then do an L to E measurement to see how much L falls in voltage with respect to local E as loading increases.

Are you able to temporarily and safely supply LG unit just via its 30mA rcd and mcb ie missing out the type S? Earth to be connected of course.

How long is the final circuit feeding LG unit?

How far away from earth electrode is the LG unit?

Please ramp test the type S RCD when on load apart from LG unit.
 
Last edited:
In LG monobloc manual:

Circuit Breaker Specification Perform the electrical wiring work according to the electrical wiring connection. • All wiring must comply with local requirements. • Select a power source that is capable of supplying the current required by the appliance. • Use a recognized ELCB(Electric Leakage Circuit Breaker) between the power source and the unit. A disconnection device to adequately disconnect all supply lines must be fitted. • Model of circuit breaker recommended by authorized personnel Only. • Select a circuit breaker suitable for the current specification.


This is as helpful as LG get!
 
In LG monobloc manual:

Circuit Breaker Specification Perform the electrical wiring work according to the electrical wiring connection. • All wiring must comply with local requirements. • Select a power source that is capable of supplying the current required by the appliance. • Use a recognized ELCB(Electric Leakage Circuit Breaker) between the power source and the unit. A disconnection device to adequately disconnect all supply lines must be fitted. • Model of circuit breaker recommended by authorized personnel Only. • Select a circuit breaker suitable for the current specification.


This is as helpful as LG get!
That's all I had to work with!
 
What is the electrical power rating of the LG unit?

What is the make and model of type s rcd?

The research I have done does not turn up an RCD type. Indeed, LG literature is silent on any special requirements for type of rcd.

Could you sketch the intake, type S, dbs, final circuits etcetera for me to study please.

I would do some N to E insulation testing of the final circuits If you have not already.

Also, could you measure voltage between N ( at main switch) to E on earth bar with a voltmeter not AVT at no load, light load, medium load and full load? Want to see if N voltage wrt local earth rises by much as loading increases.. Then do an L to E measurement to see how much L falls in voltage with respect to local E as loading increases.

Are you able to temporarily and safely supply LG unit just via its 30mA rcd and mcb ie missing out the type S? Earth to be connected of course.

How long is the final circuit feeding LG unit?

How far away from earth electrode is the LG unit?

Please ramp test the type S RCD when on load apart from LG unit.
Hi, Thank you for being so thorough. I do not have access to site and am just setting off on holiday so bare with me. Can you private message on here?
 
Hi Marconi, I have been trying to reply to your private message but am unable because of a Spam / content issue.
Very interesting, as I just experience the same issue that it trips the 100mA RCD and not 30mA RCD. Trip is from a oil filled air compressor. All measurements did not show anywhere that causes leakage. Did or have you found the fault?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Devon
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Air Source pump tripping RCD
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
SQUIGGLIES,
Last reply from
Lwhong,
Replies
22
Views
5,181

Advert

Back
Top