Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance "engineer" to commission Heat-Pump, as original company disappeared before installation. ASHP worked for a while then tripped the 100mA RCD not the 30mA. Both RCDs tested at nominal trip current and ramp test.....both passed. Selectivity obviously working fine. The supply works with a 3KW kettle and will operate with the ASHP if the earth is disconnected at the ASHP.
There is a very healthy earth to the DB.

Theories and similar experiences appreciated...........................
 
Has anyone tested the Earth leakage current at the ASHP and also at the D.B / C.U it's fed from?
What else is fed from the Local board with the 100ma S type?
 
Snowhead beat me to it - typing too slowly!

Sounds like the ASHP has developed a leak to earth. Moisture somewhere?
Have you IR tested the circuit and pump?

Sorry no similar experience - my leak was glycol not electrons 🤫
 
Hi Thanks for your input. There is a workshop and stables fed from the same protected circuit. This was the first point of call and the circuit was isolated (double pole) with no effect on the outcome. The AC side of the solar array was also isolated even though this is fed into the main phase blocks through its own DB. Earth leakage at the DB was 3.1mA, I did not test the ASHP as I presumed that would be part of the "engineer's" procedure. Ramp test for the 100mA S type RCD 72mA, and for the 30mA was 21mA. Supply cable between 100mA RCD and DB was clear and fine.
 
Well I thought that your comment that disconnecting the earth from the ASHP allowed it to run was very significant.
I don't have any suggestions as to why the 'wrong' RCD tripped!
But I think that is secondary to finding the cause of the problem.

ASHP can generate a lot of condensate, depending on how hard its working and relative humidity, although at this time of year not so much. I was just wondering if earth leakage could be self-inflicted by the ASHP on itself! Eg because of a drainage problem for example.
 
Well I thought that your comment that disconnecting the earth from the ASHP allowed it to run was very significant.
I don't have any suggestions as to why the 'wrong' RCD tripped!
But I think that is secondary to finding the cause of the problem.

ASHP can generate a lot of condensate, depending on how hard its working and relative humidity, although at this time of year not so much. I was just wondering if earth leakage could be self-inflicted by the ASHP on itself! Eg because of a drainage problem for example.
I am totally with you on that Avo. It makes no sense as the supply cables are all sound. I am hoping someone sees this who has had the same experience. All I can think of is the 100mA RCD has been damaged in a way I have never seen. It tests fine. It is an AC type as it was installed in 2018. Some HVAC guys I spoke to say they specify B Type RCDs as matter of course and that should come from the manufacturer or engineer. Although these RCDs deal more with "DC-blinding" where as in this situation, not tripping is not an issue.
 
I suspect the ASHP's inverter circuitry and associated EMC filter are producing an earth leakage current which may extend to higher frequencies than the mains 50Hz. The first thing to do is look at the ASHP's installation manual to discover what type of RCD is required. Please post full details of the ASHP so we can look up too. A quick way to find out would be to phone the ASHP manufacturer's technical help line.

Here is a short article which gives an introduction to what I suspect is happening:

Heat Pumps – Type F or Type B RCDs? - Electrical Contracting News (ECN) - https://electricalcontractingnews.com/news/heat-pumps-type-f-or-type-b-rcds/

I am not at this stage by showing you the link saying that the solution is a Type F or Type B - we need to look at the manual or contact the manufacturer first.

Note also that one cannot place a Type F or Type B downstream of a Type A or AC so it is likely your ASHP may need a dedicated supply taken from the meter output.
 
Last edited:
Further to my last: please would you use your MFT to measure and then report the Ze ( not Zs) so we can assess the site’s electrode resistance Ra. Do this at the db feeding the ashp.
 
I suspect the ASHP's inverter circuitry and associated EMC filter are producing an earth leakage current which may extend to higher frequencies than the mains 50Hz. The first thing to do is look at the ASHP's installation manual to discover what type of RCD is required. Please post full details of the ASHP so we can look up too. A quick way to find out would be to phone the ASHP manufacturer's technical help line.

Here is a short article which gives an introduction to what I suspect is happening:

Heat Pumps – Type F or Type B RCDs? - Electrical Contracting News (ECN) - https://electricalcontractingnews.com/news/heat-pumps-type-f-or-type-b-rcds/

I am not at this stage by showing you the link saying that the solution is a Type F or Type B - we need to look at the manual or contact the manufacturer first.

Note also that one cannot place a Type F or Type B downstream of a Type A or AC so it is likely your ASHP may need a dedicated supply taken from the meter output.
Hi Marconi, This was the piece of the puzzle it felt like I was missing. The company who were meant to be installing the renewables went AWOL. I had no information beyond the KW loading of the unit and some "monkey see monkey do" instructions regarding the control cables from the water cylinder and heating centre. RA on the day of testing was 11.02 Ohms.
Another avenue I was keen to explore was finding out if the delay mechanism for S Type RCDs is mechanical or analogue and if this could possibly become damaged by a malfunctioning ASHP? Thanks for your input.
 
I do not think the Type S RCD has been damaged. The S type may be more sensitive to the waveform of the earth leakage current than the 30mA RCD and thus trips first. Let us know what the ASHP manual says about type of RCD. You tested them I believe and found they operated correctly?
 
I do not think the Type S RCD has been damaged. The S type may be more sensitive to the waveform of the earth leakage current than the 30mA RCD and thus trips first. Let us know what the ASHP manual says about type of RCD. You tested them I believe and found they operated correctly?
There was nothing in the paperwork that accompanied the ASHP that referred to the supply. Also, when the "engineer" was commissioning the unit, the manufacturer's technical help-line never mentioned the type of RCD, even though they were made aware of the issue.
Both RCDs tested exactly as I would expect both on ramp and time. Selectivity was also fine with the 30mA tripping first every time.
 
Sure thank you. LG R32 Monobloc.
What is the electrical power rating of the LG unit?

What is the make and model of type s rcd?

The research I have done does not turn up an RCD type. Indeed, LG literature is silent on any special requirements for type of rcd.

Could you sketch the intake, type S, dbs, final circuits etcetera for me to study please.

I would do some N to E insulation testing of the final circuits If you have not already.

Also, could you measure voltage between N ( at main switch) to E on earth bar with a voltmeter not AVT at no load, light load, medium load and full load? Want to see if N voltage wrt local earth rises by much as loading increases.. Then do an L to E measurement to see how much L falls in voltage with respect to local E as loading increases.

Are you able to temporarily and safely supply LG unit just via its 30mA rcd and mcb ie missing out the type S? Earth to be connected of course.

How long is the final circuit feeding LG unit?

How far away from earth electrode is the LG unit?

Please ramp test the type S RCD when on load apart from LG unit.
 
Last edited:
In LG monobloc manual:

Circuit Breaker Specification Perform the electrical wiring work according to the electrical wiring connection. • All wiring must comply with local requirements. • Select a power source that is capable of supplying the current required by the appliance. • Use a recognized ELCB(Electric Leakage Circuit Breaker) between the power source and the unit. A disconnection device to adequately disconnect all supply lines must be fitted. • Model of circuit breaker recommended by authorized personnel Only. • Select a circuit breaker suitable for the current specification.


This is as helpful as LG get!
 
In LG monobloc manual:

Circuit Breaker Specification Perform the electrical wiring work according to the electrical wiring connection. • All wiring must comply with local requirements. • Select a power source that is capable of supplying the current required by the appliance. • Use a recognized ELCB(Electric Leakage Circuit Breaker) between the power source and the unit. A disconnection device to adequately disconnect all supply lines must be fitted. • Model of circuit breaker recommended by authorized personnel Only. • Select a circuit breaker suitable for the current specification.


This is as helpful as LG get!
That's all I had to work with!
 
What is the electrical power rating of the LG unit?

What is the make and model of type s rcd?

The research I have done does not turn up an RCD type. Indeed, LG literature is silent on any special requirements for type of rcd.

Could you sketch the intake, type S, dbs, final circuits etcetera for me to study please.

I would do some N to E insulation testing of the final circuits If you have not already.

Also, could you measure voltage between N ( at main switch) to E on earth bar with a voltmeter not AVT at no load, light load, medium load and full load? Want to see if N voltage wrt local earth rises by much as loading increases.. Then do an L to E measurement to see how much L falls in voltage with respect to local E as loading increases.

Are you able to temporarily and safely supply LG unit just via its 30mA rcd and mcb ie missing out the type S? Earth to be connected of course.

How long is the final circuit feeding LG unit?

How far away from earth electrode is the LG unit?

Please ramp test the type S RCD when on load apart from LG unit.
Hi, Thank you for being so thorough. I do not have access to site and am just setting off on holiday so bare with me. Can you private message on here?
 

Reply to Air Source pump tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
647
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock