meercatmag
Assuming your 10 to 20 Mohms are Megohms (as you say, measured with low voltage DC), that is probably due to superficial contamination in back boxes or humidity. It's only a matter of concern if a proper IR test at 500V revealed a value lower than one Megohm.
Those figures you report aren't a problem (within the limitations of a low voltage measurement). and would not lead to spurious tripping at a mere 10 to 20+ micro amps!
I would discourage you from roaming around the installation with an ordinary multimeter, you will probably get spurious readings from induced voltages on isolated circuits, and could inadvertently create a problem. If you are worried about the installation, get a competent electrician to do an Electrical Installation Condition Report; you will have the proper numbers from a calibrated tester, and know if there is a real issue. It's unlikely you'll need to rewire the house!
Regarding earth leakage and tripping that you queried in your first post, the evidence to me so far seems to confirm you just have an excess of leakage from small devices and accessories all fed from one RCCB.
The spec for a 30mA RCCB (or RCB) says it should trip somewhere between 15mA and 30mA leakage.
Your post #5 reports a 14mA steady leakage with washing m/c etc.
There seems to be little headroom.
These days such an installation might be wired with the kitchen on its own ring, large appliances on their own radials, probably a separate ring for each floor etc etc, and preferably RCBO's for each circuit. Adopting even minor upgrades to your installation would probably fix the tripping issue.
Just talk to a competent electrician!
Good luck.
Assuming your 10 to 20 Mohms are Megohms (as you say, measured with low voltage DC), that is probably due to superficial contamination in back boxes or humidity. It's only a matter of concern if a proper IR test at 500V revealed a value lower than one Megohm.
Those figures you report aren't a problem (within the limitations of a low voltage measurement). and would not lead to spurious tripping at a mere 10 to 20+ micro amps!
I would discourage you from roaming around the installation with an ordinary multimeter, you will probably get spurious readings from induced voltages on isolated circuits, and could inadvertently create a problem. If you are worried about the installation, get a competent electrician to do an Electrical Installation Condition Report; you will have the proper numbers from a calibrated tester, and know if there is a real issue. It's unlikely you'll need to rewire the house!
Regarding earth leakage and tripping that you queried in your first post, the evidence to me so far seems to confirm you just have an excess of leakage from small devices and accessories all fed from one RCCB.
The spec for a 30mA RCCB (or RCB) says it should trip somewhere between 15mA and 30mA leakage.
Your post #5 reports a 14mA steady leakage with washing m/c etc.
There seems to be little headroom.
These days such an installation might be wired with the kitchen on its own ring, large appliances on their own radials, probably a separate ring for each floor etc etc, and preferably RCBO's for each circuit. Adopting even minor upgrades to your installation would probably fix the tripping issue.
Just talk to a competent electrician!
Good luck.