Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
 
Remember an RCD works by seeing an imbalance in the line and neutral current.All RCD's through which the supply passes will see an imbalance and trip.
Does beg the question as to why you have ditched a perfectly good TNCS for a rubbish TT though....although I've a feeling I'm going to deeply regret asking.
 
Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
why?...

you have stated 10mm SWA...is it a 3 core?

is there extranious in the shed?

or are you another of them that say you cant extend a PME?
 
Yup. Sounds like you are supplying DB2 from a RCD protected circuit on DB1. That will always happen.
it will happen if the top end RCD...(call it RCD 1) is being subjected to leakage from other circuits its offering additional protection to....also the individual device`s characteristics being taken into account.

smells like another poor design thread to me does this...
 
New posts

Reply to DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
955
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock