Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
 
Remember an RCD works by seeing an imbalance in the line and neutral current.All RCD's through which the supply passes will see an imbalance and trip.
Does beg the question as to why you have ditched a perfectly good TNCS for a rubbish TT though....although I've a feeling I'm going to deeply regret asking.
 
Evening all

Been on here for some time now but never posted as always found the answers to my questions in older posts.

Just completing a domestic rewire with shed/office on DB2.

Installed new DB1 (split load 2 x 30mA RCDs) on new DNO TN-C-S supply. Great readings, no probs.

Run 10mm SWA to shed and installed new DB2 on a TT systm, SWA protected from DB1.

Earth spike readings are 153.3ohms. High but acceptable, if customers wallett deep enough i will install another ground spike.

Db2 supplies 2 x 20A radial ccts and 2 x 6A lighting circuits, nothing onerous there and well over the requirements needed.

When i carry out an RCD test, x1/2=good, x1 & x2 trip Db1 RCD???

Any suggestions please. What have i missed?
why?...

you have stated 10mm SWA...is it a 3 core?

is there extranious in the shed?

or are you another of them that say you cant extend a PME?
 
Yup. Sounds like you are supplying DB2 from a RCD protected circuit on DB1. That will always happen.
it will happen if the top end RCD...(call it RCD 1) is being subjected to leakage from other circuits its offering additional protection to....also the individual device`s characteristics being taken into account.

smells like another poor design thread to me does this...
 
To be honest if it was stated somewhere that you could or shouldnt then i would or wouldn't!
Didnt want RCD in house to trip and cause nuissance to customer not that it should due yo the quality of the installation yoy understand?
I have been told over the years that outbuilidings cannot use PME?
More than happy if they can, saves me a lot of work.
 
DB1 RCD protecting 3 core SWA.
3rd core CPC not connected at DB2.
DB2 25/30m away.
so...whats the problem?

rite:

for a start get back round there and get that armoured off the RCD side of that board (top end).

get rid of that bloody rod in the shed.

use one of the cores (black) as the earth...take it straight into db2s MET.

use the grey as the neutral...get all cores identified top & bottom end (colours)

you have a 10mm CSA core in the SWA...so you dont need to be pulling in a seperate G/Y..do you (just before you bothered asking)...

30mA RCD in db2 for finals in there...
 
as glenn says. use 3rd core and armour ,earthed both ends, for cpc ( and bonding if required for extraneous). extend PME and forget the rod.
 
To be honest if it was stated somewhere that you could or shouldnt then i would or wouldn't!
Didnt want RCD in house to trip and cause nuissance to customer not that it should due yo the quality of the installation yoy understand?
I have been told over the years that outbuilidings cannot use PME?
More than happy if they can, saves me a lot of work.
well then you got told a load of old chud there didn`t you...
 
I'm just wondering why he ran a 3 core 10mm cable and didn't use the the third core?? So why bother running a 3 core cable in the first place??

As far as the ''You can't extend a PME earthing system'', it's mostly down to the P**s Poor college lecturers you have in these colleges and training centers these days, that continue to perpetuate this MYTH!!
 
Nothing wrong with what he's done (except the rcd's in series) if that's how he has designed it and is happy to waste money on 3 core but not use the 3rd core to extend the pme.
Me I'd have saved some bunce and gone 2 core swa, split the tails at the house into switch fuse out in 10mm on to outbuilding small db with rcbo's

Frenchie I'm in Andover tomorrow if you want me to sort it for you.
 
I'm just wondering why he ran a 3 core 10mm cable and didn't use the the third core?? So why bother running a 3 core cable in the first place??

As far as the ''You can't extend a PME earthing system'', it's mostly down to the P**s Poor college lecturers you have in these colleges and training centers these days, that continue to perpetuate this MYTH!!
or old farts not willing to evolve! Whoops! ... Has he been provoked?...
 
or old farts not willing to evolve! Whoops! ... Has he been provoked?...

Nope is just P**s Poor college lecturers that instead of teaching if you like, just the facts, they incorporate their own ill found misconceptions!! The same goes it seems, for RFC's now being touted as dangerous!! lol!!
 
Nope is just P**s Poor college lecturers that instead of teaching if you like, just the facts, they incorporate their own ill found misconceptions!! The same goes it seems, for RFC's now being touted as dangerous!! lol!!
well eng:

i never listened to any of the old drivvel about RFCs then....and i wont now either...
and if young robert who comes out with us starts being indoctrinated by any college slavver about the `dangers` of a properly designed RFC...or how you cant extend a PME then i will be on hand to lead him back into the light...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Andover

Thread Information

Title
DB2 (TT) trips DB1 TN-C-S
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
70
Unsolved
--

Advert

Thread statistics

Created
frenchie6745,
Last reply from
Engineer54,
Replies
70
Views
7,719

Advert

Back
Top