What are peoples experience on adding the additional class II surge protection to transformerless inverters? Particuarly the sunny tripower range?

Are people finding that this is becoming a regular requirement for their installs?

I have seen a guideline regarding surge protection being required at the array as well as the inverter if there is more than 10m between the array and the inverter. What are peoples opinion of this? If I have 12 strings, this is getting very expensive. Even worse if class I is required!!

Again, any help would be greatly appreciated.
 
I always thought that you designed the invertor on your voltage open circuit x 1.25 and size the invertor accordingly. So your invertor would never suffer from DC voltage surges as it was designed to take the maximum DC that an array can ever produce, so the use of a voltage supressor seems strange.
Is it to somehow counteract the possiblilty of fault currents from the DC back into an AC side if you don't have a transformer and therefore seperation. If that was the case then you would need to somehow get an earth up to your DC side I would imagine.
 
Last edited by a moderator:
I design all DC components based on this (Voc x 1.15 and Isc x 1.25). Regarding the inverter, I design this based on the best power ratio, and also the voltage it can be exposed to at low temperatures (-10 degree C). As it is a transformerless inverter, I would bond the frames and take one connection down to earth. However I have been advised that additional class II surge protection may be required at both inverter and array.

Please see comment below from Furse:

"You mention 1.25 x Isc, which is a known safety factor for cabling, but this should not be confused with the surge current rating which may be much higher, but as a 'transient' is active for a much shorter duration; measured in microseconds.
Overvoltage is certainly your main threat, as this may cause flashover and damage within the system."

Any thoughts?
 
Well I have great respect for Furse, who sell these SPD, lol is that a coincidence.

I'm not sure where these surge currents are coming from, are they referring to fualt current ? Does an array have the capability of producing the surge currents in production. I would have thought if you had 10 panels and at maximum harvest potential they produce 2.4Kw, and you size an invertor to that with the 1,25 safety factor, can these 10 panels produce 3kw plus so give these "transient" values.

They surely though must be talking about fault currents.
 
Thanks both, apologies, yes lightning protection, protection from an indirect strike.
 
Regarding my initial query, have people been incorporating class II or I surge protection for lightning protection, either at the array or inverter?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
dc surge protection
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
paulsamuel1984,
Last reply from
paulsamuel1984,
Replies
6
Views
1,645

Advert

Back
Top