Discuss Difficult fault to find? in the UK Electrical Forum area at ElectriciansForums.net
Yes I could, but would this not just show the 1 or 2 A running through it at that time? It may change rapidly when it's about to trip but I don't think I can get away with standing there for 30 mins :)
Anyway, I am now leaving to find it!
Glad you found it! If you put 10a through a 6a mcb it will take a while to trip, and it wasn't clear if the trip was from overload or fault. The idea was also to work out if it's going down l-n or l-e or l-cpc.
Glad you're sorted though!
I think it was though. HHD reckoned on a couple of amps load on the circuit, and anything else consuming 1500VA or so would have made its presence felt. Had the MCB been tripping through being on the threshold of its current rating, a) it would have been warm which HHD would hopefully have noticed and b) the tripping would be more cyclic than random. It's useful to consider the power dissipated at a suspected fault and what damage it would cause. 1500W dissipated at a point fault would soon set it on fire or melt it so extensively that it could not have remained as it was to cause another trip. So it had to be an intermittent short-circuit, that did not blow itself clear completely on account of the low rating of the MCB and moderately high resistance of the small cable. Had the same damage occurred on a cooker circuit near the board, it would be more likely to blow itself apart at the first bang.
It had classic symptoms of a damaged cable - very low IR L-E and N-E with occasional tripping of the MCB. There was no certainty that each of the abnormal symptoms was related to a single fault but the principle of Occam's razor would suggest so. Easy to analyse with hindsight, of course.
Agree totally and thanks for the analysis, i only wanted to add it to the mix as a consideration as no point in saying "i thought that originally" after the fact!
Just a couple of points that may be interesting..
If an MCB trips in overload it can trip again quickly due to it already being very warm
Also the fault i suggested was a faulty psu for lights or similar. A transformer with shorted windings can warm up a lot without causing a fire
Reply to Difficult fault to find? in the UK Electrical Forum area at ElectriciansForums.net
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...