Discuss Disconnection times not met in the UK Electrical Forum area at ElectriciansForums.net
Three questions haha
1. 160A MCCB the max Zs for this particular switch is 0.25 ohms all tested and I’m getting 0.44 ohms its a 95 SWA outgoing which feeds another panel which has its own outgoing circuits would I be right and say that would be a code 2? As I can’t meet disconnection time on it
2. Can’t meet disconnection times for various circuits 63A MCBs no RCD protection would you code 2? Max Zs should be 0.69 ohms and I’m in the 1.00 ohms
3. If I was to add RCD to question 2 could I achieve ADS - or would I need to test L-N also for my short circuit protection
What sort of PSSC are you seeing relative to the PFC?
Those sort of numbers imply a significantly higher CPC impedance than the neutral or the voltage drop is going to be missed by a significant margin.
If it is down to the SWA armour impedance being too high (or rubbish connection to the glands/banjos), then to get the CPC impedance down a supplementary run of copper conductor along side together with decent connections at the ends might be a simpler/cheaper overall fix than changing to RCDs.
If it is down to the SWA armour impedance being too high (or rubbish connection to the glands/banjos), then to get the CPC down a supplementary run of copper conductor along side together with decent connections at the ends might be a simpler/cheaper overall fix than changing to RCDs.
Hi, thanks for the reply it’s a small site with some 20 caravan boxes so all SWA cable and underground, I’m just wanting to make sure my coding is right
[automerge]1594229615[/automerge]
Where have you got your maximum Zs rating from?
Manufactures data
That is a good point, just checked and a 63A B-curve MCB should be 0.56 ohms from OSG.
MCCB are more of a pain as you need to look up a specific model (and/or what settings are dialled in to it) but scaling a 100A B-curve MCB points to 0.21 ohm as being more likely for a 160A device.
[automerge]1594230137[/automerge]
Manufactures data
Interesting, as Wylex have this for their miniature 63A MCB:
  • B-curve 0.729 ohm
  • C-curve 0.364 ohm
  • D-curve 0.183 ohm
Would I be right for saying code 2 for questions 1 and 2? Is it just poor design for TNS system
[automerge]1594230270[/automerge]
  • B-curve 0.729 ohm
  • C-curve 0.364 ohm
  • D-curve 0.183 ohm
I have an app on my phone, plus I’m on the NIC certs so auto puts a maximum reading in for MCBs etc
Yes, that would be right. According to the Best Practice Guide #4 it is C2 for:
Earth fault loop impedance value greater than that required for operation of the protective device within the time prescribed in the version of BS 7671/IEE/IET Wiring Regulations or manufacturers’ published data current at the time of installation
You could work out the R1+R2 rating for the cable run and see how it compares with your measured Zs minus Ze. If it's similar it's a good reading and something needs sorting. If not, it could be a bad connection.
As a carven park I guess most end circuits have RCDs anyway, so you could deal with the (probably) high R2 by going to delay RCDs and/or a delay RCD add-on to the MCCB, but first it would be worth finding out if it is simply too much cable/not enough armour, or if there is some crappy gland use to be fixed.
[automerge]1594230720[/automerge]
I was just unsure as the 160A MCCB feeds the panel with 63A MCBs but the Max Zs is higher than the Max Zs of the 160A MCCB thought it was a C2
Is it feeding just the internal bus of the panel? I.e. there is no cables longer than 3m coming from the MCCB?
If so then the issue is one of meeting disconnection times on the 63A outgoing circuit MCBs, as the MCCB is only needed for overall overload of the system if (as is likely) the sum of MCBs exceeds the supply capability. I.e. no C2 code on the MCCB as it is not providing earth fault protection anyway.
Yes I spoke to my boss and he’s on about putting a 300mA time delayed RCD inside panel with the MCBs as each box has its own 30mA additional protection as all readings are similar and get higher towards ends of circuits
[automerge]1594230810[/automerge]
But he didn’t say anything about the 160A MCCB feeding the panel as that is 0.20 ohms higher???
[automerge]1594230931[/automerge]
So the 160A MCCB feeds the panel with 95 SWA to some bolts ons that feeds a 100A isolator and 63A MCBs
I think we are getting to the "we need a diagram" stage of the thread!
If the MCCB is feeding stuff beyond a well-protected cable less than 3m in length then it ought to meet fault to earth disconnection times.
I was thinking of a MCCB incomer to a board: in that case the MCCB need not meet disconnection on its own, as all circuits ought to be met by the outgoing MCBs' protection.
Okkkk,
Yes so 160A MCCB fed from EB tails, 40 metre ish run of 95 SWA to the Panel with all outgoing 63A MCBs haha
[automerge]1594231588[/automerge]
So disconnection only applies to final circuits? Thanks so far not really done much with coding and testing
I've got an old table indicating that the csa of 95mm armouring may not be sufficient. I still go by it but it may be a bit dated.
Thanks for that
[automerge]1594232508[/automerge]
Spoke to another guy and he says C2 for the 160A MCCB as it still needs to disconnect in 5s if ever someone went through the cable??
[automerge]1594233780[/automerge]
Thanks for that
But I have no idea haha
That table only shows the basic method of working out CPC size by selection from a table.
If you do the adiabatic calculation you will find that with almost all of those cable sizes the armour will comply as a CPC.
[automerge]1594234223[/automerge]
It applies to all circuits, distribution and final.
What pc1966 is saying is that they thought you were talking about a 160A MCCB fitted as a main switch in a DB which is a different situation.
[automerge]1594234522[/automerge]
What is the job you are doing?
If you are doing an EICR then you code it appropriately (C2 in this case) and submit the report leaving it up to whoever is quoting for the remedial works to come up with a plan to fix it.
If you are doing an EICR and also quoting for any remedial work that comes as a result of it then you still complete the EICR before planning the remedials.
If I was looking at the remedial work for this I would first be checking the Ze and checking all cpc connections for soundness. Then I would look at whether replacing the 160A MCCB with a fused switch would be a viable solution and similar with the 63A MCB's.
Yes, to add to what @davesparks said - when you have the cable fed from the MCCB it should meet the disconnection time of 5s for the end Zs value just in case there is damage at any point along the cable. My earlier comment was just as he said - for a MCCB incomer.
Changing the MCCB to include RCD capability would be one fix. However if you get one of the fancier MCCB you might be able to configure the over-current trip curve to meet 5s for your cable-end Zs of 0.44 ohm (say setting it to trip at 5s for 0.95 * 230 / 0.44 = 496A) so you meet cable disconnection, your "instant trip" is still well beyond any downstream MCB for selectivity, and you are not having to find space for a MCCB add-on module.
I don't know enough about the details of MCCB selection to say for sure, probably @Julie. or @davesparks would have a lot more knowledge than me for this aspect.
[automerge]1594235027[/automerge]
Me? Talking nonsense on internet forums seem to be my current status.
At least I keep my clothes on for this forum :)
Thanks for your help guys, yes my only concern or lack of knowledge was the MCCB and the Zs value I got which was exceeding the Max values allowed, now the MCCB has 3 settings 125A, 140A, 160A but I believe even setting on 125A I won’t be achieving the values I was getting,
So just to confirm it would be a C2 on report? Sorry I’m trying to understand incase I come into this situation again
Reply to Disconnection times not met in the UK Electrical Forum area at ElectriciansForums.net
Simple question (or so I thought) What would be the Correct OCPD to achieve correct disconnect times for a 200amp sun-main with ze of 0.26 tncs...
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
OLDBOY
O
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...