Three questions haha
1. 160A MCCB the max Zs for this particular switch is 0.25 ohms all tested and I’m getting 0.44 ohms its a 95 SWA outgoing which feeds another panel which has its own outgoing circuits would I be right and say that would be a code 2? As I can’t meet disconnection time on it
2. Can’t meet disconnection times for various circuits 63A MCBs no RCD protection would you code 2? Max Zs should be 0.69 ohms and I’m in the 1.00 ohms
3. If I was to add RCD to question 2 could I achieve ADS - or would I need to test L-N also for my short circuit protection