1. 160A MCCB the max Zs for this particular switch is 0.25 ohms all tested and I’m getting 0.44 ohms its a 95 SWA outgoing which feeds another panel which has its own outgoing circuits would I be right and say that would be a code 2? As I can’t meet disconnection time on it

2. Can’t meet disconnection times for various circuits 63A MCBs no RCD protection would you code 2? Max Zs should be 0.69 ohms and I’m in the 1.00 ohms

3. If I was to add RCD to question 2 could I achieve ADS - or would I need to test L-N also for my short circuit protection
 
What sort of PSSC are you seeing relative to the PFC?

Those sort of numbers imply a significantly higher CPC impedance than the neutral or the voltage drop is going to be missed by a significant margin.

If it is down to the SWA armour impedance being too high (or rubbish connection to the glands/banjos), then to get the CPC impedance down a supplementary run of copper conductor along side together with decent connections at the ends might be a simpler/cheaper overall fix than changing to RCDs.
 
Where have you got your maximum Zs rating from?
 
What sort of PSSC are you seeing relative to the PFC?

Those sort of numbers imply a significantly higher CPC impedance than the neutral or the voltage drop is going to be missed by a significant margin.

If it is down to the SWA armour impedance being too high (or rubbish connection to the glands/banjos), then to get the CPC down a supplementary run of copper conductor along side together with decent connections at the ends might be a simpler/cheaper overall fix than changing to RCDs.
Hi, thanks for the reply it’s a small site with some 20 caravan boxes so all SWA cable and underground, I’m just wanting to make sure my coding is right
[automerge]1594229615[/automerge]
Where have you got your maximum Zs rating from?
Manufactures data
 
  • Like
Reactions: ipf
Where have you got your maximum Zs rating from?
That is a good point, just checked and a 63A B-curve MCB should be 0.56 ohms from OSG.

MCCB are more of a pain as you need to look up a specific model (and/or what settings are dialled in to it) but scaling a 100A B-curve MCB points to 0.21 ohm as being more likely for a 160A device.
[automerge]1594230137[/automerge]
Manufactures data
Interesting, as Wylex have this for their miniature 63A MCB:
  • B-curve 0.729 ohm
  • C-curve 0.364 ohm
  • D-curve 0.183 ohm
 
Would I be right for saying code 2 for questions 1 and 2? Is it just poor design for TNS system
[automerge]1594230270[/automerge]
That is a good point, just checked and a 63A B-curve MCB should be 0.56 ohms from OSG.

MCCB are more of a pain as you need to look up a specific model (and/or what settings are dialled in to it) but scaling a 100A B-curve MCB points to 0.21 ohm as being more likely for a 160A device.
[automerge]1594230137[/automerge]

Interesting, as Wylex have this for their miniature 63A MCB:
  • B-curve 0.729 ohm
  • C-curve 0.364 ohm
  • D-curve 0.183 ohm
I have an app on my phone, plus I’m on the NIC certs so auto puts a maximum reading in for MCBs etc
 
Would I be right for saying code 2 for questions 1 and 2? Is it just poor design for TNS system
Yes, that would be right. According to the Best Practice Guide #4 it is C2 for:

Earth fault loop impedance value greater than that required for operation of the protective device within the time prescribed in the version of BS 7671/IEE/IET Wiring Regulations or manufacturers’ published data current at the time of installation
 
  • Like
Reactions: ipf
You could work out the R1+R2 rating for the cable run and see how it compares with your measured Zs minus Ze. If it's similar it's a good reading and something needs sorting. If not, it could be a bad connection.
 
If it is down to the SWA armour impedance being too high (or rubbish connection to the glands/banjos),
this what i was thinking on the same lines .
 
  • Like
Reactions: pc1966
I was just unsure as the 160A MCCB feeds the panel with 63A MCBs but the Max Zs is higher than the Max Zs of the 160A MCCB thought it was a C2
 
As a carven park I guess most end circuits have RCDs anyway, so you could deal with the (probably) high R2 by going to delay RCDs and/or a delay RCD add-on to the MCCB, but first it would be worth finding out if it is simply too much cable/not enough armour, or if there is some crappy gland use to be fixed.
[automerge]1594230720[/automerge]
I was just unsure as the 160A MCCB feeds the panel with 63A MCBs but the Max Zs is higher than the Max Zs of the 160A MCCB thought it was a C2
Is it feeding just the internal bus of the panel? I.e. there is no cables longer than 3m coming from the MCCB?

If so then the issue is one of meeting disconnection times on the 63A outgoing circuit MCBs, as the MCCB is only needed for overall overload of the system if (as is likely) the sum of MCBs exceeds the supply capability. I.e. no C2 code on the MCCB as it is not providing earth fault protection anyway.
 
As a carven park I guess most end circuits have RCDs anyway, so you could deal with the (probably) high R2 by going to delay RCDs and/or a delay RCD add-on to the MCCB, but first it would be worth finding out if it is simply too much cable/not enough armour, or if there is some crappy gland use to be fixed.
Yes I spoke to my boss and he’s on about putting a 300mA time delayed RCD inside panel with the MCBs as each box has its own 30mA additional protection as all readings are similar and get higher towards ends of circuits
[automerge]1594230810[/automerge]
Yes I spoke to my boss and he’s on about putting a 300mA time delayed RCD inside panel with the MCBs as each box has its own 30mA additional protection as all readings are similar and get higher towards ends of circuits
But he didn’t say anything about the 160A MCCB feeding the panel as that is 0.20 ohms higher???
[automerge]1594230931[/automerge]
As a carven park I guess most end circuits have RCDs anyway, so you could deal with the (probably) high R2 by going to delay RCDs and/or a delay RCD add-on to the MCCB, but first it would be worth finding out if it is simply too much cable/not enough armour, or if there is some crappy gland use to be fixed.
[automerge]1594230720[/automerge]

Is it feeding just the internal bus of the panel? I.e. there is no cables longer than 3m coming from the MCCB?

If so then the issue is one of meeting disconnection times on the 63A outgoing circuit MCBs, as the MCCB is only needed for overall overload of the system if (as is likely) the sum of MCBs exceeds the supply capability. I.e. no C2 code on the MCCB as it is not providing earth fault protection anyway.
So the 160A MCCB feeds the panel with 95 SWA to some bolts ons that feeds a 100A isolator and 63A MCBs
 
So the 160A MCCB feeds the panel with 95 SWA to some bolts ons that feeds a 100A isolator and 63A MCBs
I think we are getting to the "we need a diagram" stage of the thread!

If the MCCB is feeding stuff beyond a well-protected cable less than 3m in length then it ought to meet fault to earth disconnection times.

I was thinking of a MCCB incomer to a board: in that case the MCCB need not meet disconnection on its own, as all circuits ought to be met by the outgoing MCBs' protection.
 
I think we are getting to the "we need a diagram" stage of the thread!

If the MCCB is feeding stuff beyond a well-protected cable less than 3m in length then it ought to meet fault to earth disconnection times.

I was thinking of a MCCB incomer to a board: in that case the MCCB need not meet disconnection on its own, as all circuits ought to be met by the outgoing MCBs' protection.
Okkkk,
Yes so 160A MCCB fed from EB tails, 40 metre ish run of 95 SWA to the Panel with all outgoing 63A MCBs haha
[automerge]1594231588[/automerge]
So disconnection only applies to final circuits? Thanks so far not really done much with coding and testing
 
I've got an old table indicating that the csa of 95mm armouring may not be sufficient. I still go by it but it may be a bit dated.

IMG_0362.jpg
 
  • Like
Reactions: pc1966
I've got an old table indicating that the csa of 95mm armouring may not be sufficient. I still go by it but it may be a bit dated.

View attachment 59330
Thanks for that
[automerge]1594232508[/automerge]
Spoke to another guy and he says C2 for the 160A MCCB as it still needs to disconnect in 5s if ever someone went through the cable??
[automerge]1594233780[/automerge]
Thanks for that
[automerge]1594232508[/automerge]
Spoke to another guy and he says C2 for the 160A MCCB as it still needs to disconnect in 5s if ever someone went through the cable??
But I have no idea haha
 
Last edited:
I've got an old table indicating that the csa of 95mm armouring may not be sufficient. I still go by it but it may be a bit dated.

View attachment 59330

That table only shows the basic method of working out CPC size by selection from a table.
If you do the adiabatic calculation you will find that with almost all of those cable sizes the armour will comply as a CPC.
[automerge]1594234223[/automerge]
So disconnection only applies to final circuits? Thanks so far not really done much with coding and testing

It applies to all circuits, distribution and final.

What pc1966 is saying is that they thought you were talking about a 160A MCCB fitted as a main switch in a DB which is a different situation.
[automerge]1594234522[/automerge]
Yes I spoke to my boss and he’s on about putting a 300mA time delayed RCD inside panel with the MCBs as each box has its own 30mA additional protection as all readings are similar and get higher towards ends of circuits

But he didn’t say anything about the 160A MCCB feeding the panel as that is 0.20 ohms higher???

So the 160A MCCB feeds the panel with 95 SWA to some bolts ons that feeds a 100A isolator and 63A MCBs

What is the job you are doing?
If you are doing an EICR then you code it appropriately (C2 in this case) and submit the report leaving it up to whoever is quoting for the remedial works to come up with a plan to fix it.
If you are doing an EICR and also quoting for any remedial work that comes as a result of it then you still complete the EICR before planning the remedials.

If I was looking at the remedial work for this I would first be checking the Ze and checking all cpc connections for soundness. Then I would look at whether replacing the 160A MCCB with a fused switch would be a viable solution and similar with the 63A MCB's.
 
Last edited by a moderator:
  • Like
Reactions: pc1966
Yes, to add to what @davesparks said - when you have the cable fed from the MCCB it should meet the disconnection time of 5s for the end Zs value just in case there is damage at any point along the cable. My earlier comment was just as he said - for a MCCB incomer.

Changing the MCCB to include RCD capability would be one fix. However if you get one of the fancier MCCB you might be able to configure the over-current trip curve to meet 5s for your cable-end Zs of 0.44 ohm (say setting it to trip at 5s for 0.95 * 230 / 0.44 = 496A) so you meet cable disconnection, your "instant trip" is still well beyond any downstream MCB for selectivity, and you are not having to find space for a MCCB add-on module.

I don't know enough about the details of MCCB selection to say for sure, probably @Julie. or @davesparks would have a lot more knowledge than me for this aspect.
[automerge]1594235027[/automerge]
What is the job you are doing?
Me? Talking nonsense on internet forums seem to be my current status.

At least I keep my clothes on for this forum :)
 
  • Funny
Reactions: DPG
Thanks for your help guys, yes my only concern or lack of knowledge was the MCCB and the Zs value I got which was exceeding the Max values allowed, now the MCCB has 3 settings 125A, 140A, 160A but I believe even setting on 125A I won’t be achieving the values I was getting,


So just to confirm it would be a C2 on report? Sorry I’m trying to understand incase I come into this situation again
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Disconnection times not met
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Julie.,
Replies
29
Views
6,625

Advert