Revamping a Classroom for cookery,originally 9 cookers @ 10kw…adding 2 more total 11.
Existing TPN DB 100 amps.
Seems a bit overloadEd don’t you think…would you mention this to the Client..or just not install the extra cookers.
We have no design input on this one,like I said originally 9 cookers.
 
thinking cooker diversity, you should be OK> split as best you can between the 3 phases. or.... uprate the supply.
 
Just been through this, adding 2x 12kW 3-phase ovens, on a supply that already can be overloaded at times, certainly need to discuss with client. The client is considering upgrading the supply but the costs are somewhat high (DNO suggesting customer has to pay tens £k to upgrade DNO's network /transformer). In this case, in the meantime, client knows to avoid using some other high current equipment at the same time (yes, I know, this will get forgotten in time).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Diversity the dance group?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
littlespark,
Replies
4
Views
1,162

Advert

Back
Top