I have a site with a three phase service head with only a single phase in use via a single phase meter.

20200814_124345.jpg


Phoned the DNO,

"This is a job for the supplier."

Phoned the supplier.

"Won't touch the service head as its DNO property."

Phoned the DNO back,

"Send us a picture we'll have a look"

I can't believe this is a rare occurrence, when will they get their act together?
 
What is it you are trying to achieve, a three phase supply or 3 single phase supplies? Did you ask the supplier for a three phase meter? If you want to get extra supplies you are into MPAN number territory. I am guessing it is SSE you are dealing with?
 
I am confused, what exactly do you want them to do for you?
 
first need to check if 3 phases are connected in service head. if so, it's down to supplier to fit and connect 3 phase meter. if not, DNO to connect the other 2 phases first.
 
Thats the DNO not the supplier thought isn't it
An iso is neither, weirdly. Because it's down-stream of the meter it classes as part of the consumers installation, and in the early days of part pish a lot of DNO's / Energy suppliers were refusing to fit them..... because.... they weren't Part P registered. You really can't make this crap up ?
 
N
What is it you are trying to achieve, a three phase supply or 3 single phase supplies? Did you ask the supplier for a three phase meter? If you want to get extra supplies you are into MPAN number territory. I am guessing it is SSE you are dealing with?
No, just a three phase meter on the same MPAN.
 
first need to check if 3 phases are connected in service head. if so, it's down to supplier to fit and connect 3 phase meter. if not, DNO to connect the other 2 phases first.
I had the head replaced earlier in the year, three phases are connected.
 
In that case I would check what was requested from the supplier.

If the customer requested a standard connection, then that would be single phase, in fact some suppliers will only provide single phase contracts.

You need a three phase meter, or indeed three single phase meters - but that choice is up to the supplier - When you contract to a supplier for a three phase supply they need to organise the correct metering.

Who fitted the meter - what was there before?
 
Agree with @Julie.
If your customer asked for a 3x 100A supply then thats what you should have (providing it was agreed)

If they have not requested anything other than a supply then they will get the standard for the area, normally 100A single phase but some areas i think are still putting in 80A supplies.
 
I've made a right ar5e of this thread.

The single phase supply off the three phase head has been the only supply in recent memory.

The new looking head is on account of a bitumin leak in the old head leading to a new head fit, this why we know its three live connected phases.

The bitumin leak was probably due to brief periods of overload which fits with the load assessment I did a year ago but they were unwilling to stop the business to remedy.

In the last eight months the site has closed as the building was deemed unsafe and a period of demolishing and rebuilding ensued.

Eventually the top two floors of the building were pretty much removed and rebuilt leading to them requiring rewiring.

This gave us the opportunity to upgrade the gas heating and extend it into the new floors, LED all lights and thus remove approx 25A of load.

Slowly this load saving has been chewed into by fitting more business capacity putting us back up into a situation where it is reasonable to expect periods of overload again.


So, we now want the other two phases brought online.