Nothing wrong with your current setup. You have a split CU where the 5 circuits on the left are RCD protected and the 5 on the right are not. It is a standard 5+5 CU as normally installed prior to 2008.The present configuration has 1 RCD way spare,and 2 non-RCD ways spare. Any alterations and additions carried out as part of your extension will almost certainly require RCD protecting. RCBO's can be used on the non-RCD side,and as long as there are enough spare ways for new circuits then there is no need to replace the CU.
If more ways than the 3 spare are required then changing the CU for a larger capacity unit may be the preferred option,alternatively a separate CU for the new circuits could be installed and the existing left alone.