C2 for labelling says it all for me. I don't even mention labels, I tend to just add them.
Also lots of mention of non compliance for RCDs yet has RCD test times for nearly all circuits yet no mention of RCDs anywhere on the circuit details or anywhere else.
I hate it when inspectors do not expand on the faults found either, SELV/PELV requirements so either a shaver socket or extra low voltage lighting faulty? Or is it because the 12 volt lamp holder is not earthed?
I probably know the answer already but do you have a photo of the consumer unit?
Also lots of mention of non compliance for RCDs yet has RCD test times for nearly all circuits yet no mention of RCDs anywhere on the circuit details or anywhere else.
I hate it when inspectors do not expand on the faults found either, SELV/PELV requirements so either a shaver socket or extra low voltage lighting faulty? Or is it because the 12 volt lamp holder is not earthed?
I probably know the answer already but do you have a photo of the consumer unit?