Hi,
Apologies if this has been posted before which I expect it has but did a search and couldn't find it. Wabt a bit of information on SPD's in domestic premises when carrying out a consumer unit change. Do we have to recommend they are installed now and if not carry out a risk assessment or are we ok not to carry out a risk assessment as its a single dwelling? Also am I right in thinking its a type. 1 that mounts in a din rail enclosure and if so does anyone have a decent wiring diagram. Did a bit of research but still unclear.
Many thanks
Hi,
Many thanks
What was the results of your research? Regulation 534.1 Appendix 16 table 534.4.10 and table OSG 3.7.3 refers.
It would be a type 2 SPD.
Type 1 SPD’s are used in installations with lightning protection.
It’s a conversation to be had with your customer as they are not mandatory for domestic single dwellings where the losses of equipment are tolerable Where SPD’s are not installed.
Offer it to your customer and if they decline then so be it.
Note it on the EIC
No risk assessment for domestic, you fit one or you do not ,based on the equipment it protects.
Wiring diagrams are given in appendix 16 of bs7671 and you can get manufacturers instructions/ diagrams
So fed from a breaker then from within the consumer unit. What size breaker? Sorry its just easier to ask on here and get direct responses, appreciate the advice from you all
A type 2 cpc connection must be 6mm2 minimum.
Connections should ideally not exceed 0.5m but must not exceed 1 meter in length ie the live and cpc conductors in total combined.
The ocpd need only provide fault protection.
If on the load side of an rcd the rcd should be an S type with an immunity to surges of 3ka
main switch >> 32a MCB
6mm out the load of the 32a MCB and a 6mm out the N bus bar
domestic will be a type 2 SPD at the DB
my interpretations is becuase the total value of the installation will in most if not all cases exceed the cost of what it would cost to install a SPD (an additional £60+ odd quid in materials when installing a new DB)
therfore 443.4 is not a get out of free card in my eyes
i see it the only way to get out of not installing a SPD when installing a new DB is doing the risk assessment- but good luck doing that accurately and with confidence
main switch >> 32a MCB (need a high integrity board if it dual rcd)
The CRL risk assessment is not applicable to domestic single dwelling units
Fitting one is as you say , is based on an assessment of what it’s protecting and cost.