I'm back, thank you Ristard and Biff!

Just because an item of equipment is double insulated, that doesn't mean that this is your protective measure because you are still relying on ADS for the rest of the circuit. Double insulation of an accessory and double insulation used as a sole protective measure are poles apart!

The box I am talking about should only be ticked when a whole installation or part of it relies on double insulation as its sole protective measure. Now the only people I know of who use this type of protective measure are Network Rail and TFL (if anyone knows any others feel free to add :)).

Double or reinforced insulation as a sole protective measure renders earthing, RCDs, cpcs etc.. meaningless. It can also only be used when an installation is under supervision under normal use which means that it will never be found in any domestic setting 412.1.3.

The above also applies to SELV and PELV. Just because you may have fitted some SELV downlights in your house, that doesn't mean that you are relying on SELV as your sole protective measure.

For anyone in doubt please look at the example schedule of inspections towards the back of GN3!
 
Why then does it says "MethodS of protection" - it doesn't say sole or even primary?

The other sections require multiple ticks dependant on what is present.
 
Because there is more than one method to choose from. The box referrs to the protective measure of the circuit or installation.

If the installation's protective measure is ADS, you are not relying on double or reinforced insulation as a protective measure on one light fitting that happens to be class 2. You are still relying on ADS.

Look at the protective measure for electrical separation, it's split into two I believe for the very same reason.
 
you need to look at the context in which the information is requested.

the method of protection against shock section is the very first item on the S.O.I sheet.
which suggests its very important , yes ?

so , given its primary position in the checklist suggests thats its asking to be recorded the general , over-riding means of achieving shock protection which may act as an alterative to ADS, not as a means of recording that youve stuck in a couple of class 2 fittings somewhere.

And to answer geoffs question , i imagine theyve used method(s) in plurel is because its theoretically possible to rely on a combination of 2 or more of the methods for more specialized and seldom encountered installations whose design and contruction isnt entirely covered by bs7671 alone.
 
Years ago, my tutor/lecturer said tick if there are any double insulated items. i.e. kite marked class II square in square. Never thought to doubt him.
 
how many houses burnt down before you found out differently ?




;-)

Three I think. Only one death though so it's all good :D

Seriously though, I always have and always will use MCBs and fuses for overcurrent/short circuit protection (unless not needed for whatever reason), so at that time, my lack of knowledge on that one particular subject posed no risk to anyone.

Still embarrasing though!
 
Cheers, think I may have been making a fool of myself with the SoI, but hey never mind, wont do it again, promise....:freak:

I think one of the problems here is the interpretation of badly worded thrases, which could be interpreted in so many different ways........infact if you made your own certs (and I do) you could base them around BS7671 but change the wording yourself, if your brave enough. Also have a look at Part P Doctor if you have a copy.....he informs that if SELV down lights, shaver points and classII light fittings are installed then tick the appropriate box in the basic and fault protection bit......or was that a dream!:goofy:
But at the end of the day, does it make much difference, we all would know, that even if the double insulation box was ticked for a domestic and vast majority of commercial installations, that ADS was the primary method of protection.

Hey why do I get logged off when trying to post......annoying!
 
Don't wish to take this off topic, but there must be a few electrical companies out there with a tick fetish.......take for example a London based company......EICR Schedule of Test Results......continuity of circuits, IR and Zs all 'ticked'.
 
Also have a look at Part P Doctor if you have a copy.....he informs that if SELV down lights, shaver points and classII light fittings are installed then tick the appropriate box in the basic and fault protection bit......or was that a dream!

A dream I'm afraid lol.

He specifically says that he won't cover this section because there will never be a tick in any of these four boxes in a domestic situation.
 