Wiring a 2.2kw electric oven.. instruction manual states for warranty to be valid needs a double pole control unit.
There is a double socket inside one of the cubbords; is it ok to spur of this double socket to feed the double pole control unit?
 
Easier than that:- Make sure or change the socket to a DP switched socket and just plug the oven plug top in. All regs are met.
 
Last edited by a moderator:
Easier than that:- Make sure or change the socket to a DP switched socket and just plug the oven plug top in. All regs are met.

The socket doesn't need to be switched at all, pulling a plug out gives a far better isolation gap than any switch will
 
Wiring a 2.2kw electric oven.. instruction manual states for warranty to be valid needs a double pole control unit.
There is a double socket inside one of the cubbords; is it ok to spur of this double socket to feed the double pole control unit?
How is the DP socket wired, is it a spur from a ring final?? recommendations are that 2KW and above are fed from their own individual circuit.
 
The socket doesn't need to be switched at all, pulling a plug out gives a far better isolation gap than any switch will

IMO the socket should be un switched in this case though or a double pole switched socket like Paul said.
 
Last edited by a moderator:
first we need to know if this oven has a factory fitted plug or not.
 