I would think you are unlikely to source one easily (lack of demand) as the permitted Zs values would be too low and unlikely that you could satisfy them unless you sat it on the incomming cutout feeding an adjacent load or oversized the cables plus extra earthing on a run of any distance, if you get the picture :wink5:
 
Last edited by a moderator:
Double pole MCBs are available, they are just two single pole MCBs stuck together in the same manner as triple pole or 3 phase MCBs.
Normally used for 110V split phase installations.
 