I haven't read the whole thread Andy, but I doubt theres anyone who has agreed with the Code 2's.
I agree with you and dont think there should be any code for the 3 things you have mentioned.

BS3036 fuses are still in BS7671 so as long as they meet Zs times then they are fine.
As for the 6mm bonding and 10mm ME, have a look at the Best Practice Guide 6 (page 5, section 6.1 notes 2&3) It states the following:

2. A 6 mm2 or 10 mm2 earthing conductor used with an
associated line conductor of 25 mm2 could be considered
adequate if the requirements of Regulation 543.1.3 are met.

3. A 6 mm2 main protective bonding conductor size could be
deemed adequate where the minimum size required by
Regulation 544.1.1 of BS 7671 is 10 mm2, if the bonding
conductors have been in place for a significant time and show
no signs of thermal damage.

http://www.----------------------------/mediafile/100126672/Best-Practice-Guide-6.pdf

That should be enough ammunition for you :smile5:
 
  • Like
Reactions: 1 person

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Doubtful EICR
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
20

Thread Tags

Advert

Thread statistics

Created
Andy78,
Last reply from
HappyHippyDad,
Replies
20
Views
254

Advert