I think it's highly unlikely that you'll ever get to see a correctly recorded EICR, they must be as rare as Hens Teeth from what i can make of it!! lol!!

Especially not when you consider the majority of new works completed nowadays mostly domestic wouldn't even get a satisfactory outcome let alone places 20 years + !!
 
In the absence of understanding across the industry AND more improtantly with clients my point of reference is the Best Practice Guide from the electrical safety council.

Like it or not, at least its something a customer can access and read:

Best Practice Guides | Electrical Safety First
 
This is a good publication anybody doing EICR reporting should carry this although the scammer schemes do not look favourably on some of its content yet they still endorse it.
 
In the absence of understanding across the industry AND more improtantly with clients my point of reference is the Best Practice Guide from the electrical safety council.

Like it or not, at least its something a customer can access and read:

Best Practice Guides | Electrical Safety First

I have referenced this as well as the regs within my letter and attached a pdf copy of the best practice guide too.
It helps that the inspecting company's own scheme are stated as contributors to and endorsers of the guide. :)
 
I haven't read the whole thread Andy, but I doubt theres anyone who has agreed with the Code 2's.
I agree with you and dont think there should be any code for the 3 things you have mentioned.

BS3036 fuses are still in BS7671 so as long as they meet Zs times then they are fine.
As for the 6mm bonding and 10mm ME, have a look at the Best Practice Guide 6 (page 5, section 6.1 notes 2&3) It states the following:

2. A 6 mm2 or 10 mm2 earthing conductor used with an
associated line conductor of 25 mm2 could be considered
adequate if the requirements of Regulation 543.1.3 are met.

3. A 6 mm2 main protective bonding conductor size could be
deemed adequate where the minimum size required by
Regulation 544.1.1 of BS 7671 is 10 mm2, if the bonding
conductors have been in place for a significant time and show
no signs of thermal damage.

http://www.----------------------------/mediafile/100126672/Best-Practice-Guide-6.pdf

That should be enough ammunition for you :smile5:
 