A

Andy78

I was given a couple of EICRs by a colleague today to peruse. They both pertain to rented properties and both have similar recommendations. Both supplies are TNC-S, both 16mm supply conductors, both 10mm main earth and 6mm main bonding. They have issued C2 for all of the following issues

  • Use of 3036 board - requires upgrading
  • main earth conductor too small
  • main bonding conductor too small
I am am maintaining that all of these should be given no code at all, and the "specialist testing company" is trying it on to gain a bit of work. I am in the middle of helping my colleague construct a letter that questions the findings of these EICRs to the benefit of the client who is currently considering taking this company on for the remedial work and two further EICRs.

I have referenced the regs which state that previous installations require no upgrading unless unsafe, and the ESC EICR guide which state that use of 3036 boards and minimum 6mm main bonds should not attract any code.

Can anyone help back me up my viewpoint with anything I may have missed, or indeed does anyone disagree with my stance ?
 
Well there is nothing at all wrong with 16mm tails if the incoming fuse is rated at 60A.
The 10mm2 main earth conductor would only warrant a C3 departure.
The 6mm bonding would also only warrant a C3 so long as there are no signs of overheating and deterioration of the cable at its point of connection to the service it is bonded to.
It appears that the EICR has been completed by somebody not well versed in carrying out reports or with limited knowledge of what constitutes a dangerous condition or something that although doesn't comply with current standards still is fit for ongoing use.
 
There are a few more Trev, but mainly relating to test results, and without being able to visit the properties and inspect and test myself I'm not willing to include those.
 
EICR reporting over the last few years since the introduction of the Electrical Trainee courses has become a joke sadly.
 
I have lost count of the number of reports i have seen where because circuitry has no RCD in a bathroom on an older installation it automatically becomes dangerous and gets given an unsatisfactory outcome.
 
I see a code 2 on an EICR the other day because the DB had an upfront RCD ! The customer showed me the quote for the remedial work but folded the company headed paper over so couldn't see what company it was. £900 to replace DB with main switch board and 4 RCBO's as only 4 circuits,replace 2x 2gang sockets and replace 1x Baton holder what a rip off! Any way the customer said I only used him because I got recommended him from a certain estate agent, as soon as she said that I knew who it was and he got his comeuppance in the wholesalers the other morning the robbing b***ard:icon12:
 
Last edited by a moderator:
W@nkers.

I used to subby for a testing company and they were dishing out old code 2s for a 20A breaker on hotel room RFCs.
When I took over the job and stopped coding, the work seemed to dry up!!!

W@nkers.
 
W@nkers.

I used to subby for a testing company and they were dishing out old code 2s for a 20A breaker on hotel room RFCs.
When I took over the job and stopped coding, the work seemed to dry up!!!

W@nkers.

Pure case of 'oh it doesn't say in the regs you can use a 20A mcb on a ring so it must be "DANGEROUS" '[emoji23][emoji23]
 
Letter containing my findings with reference to the regs will be sent in the morning. We'll see how it goes.
 
When I do an EICR or make any notes of departures etc I always write the rev number next to it so you can see where I got it from.
 
When I do an EICR or make any notes of departures etc I always write the rev number next to it so you can see where I got it from.

Exactly what i used to do until the scammer scheme inspector told me to refrain from doing so as it "would cause confusion to the average person ordering the report seeing rows of numbers and symbols which mean nothing to them"
 
Pure case of 'oh it doesn't say in the regs you can use a 20A mcb on a ring so it must be "DANGEROUS" '[emoji23][emoji23]

It's pathetic!
I've always wondered what happened, half the hotel was coded 2, then the other half was clear :smilielol5:
Also, every inaccessible room CU was coded 3 because they didn't have a 'WARNING 230 VOLTS' sticker on them.


Name and shame..............
a Chesterfield testing company.
 
I think it's highly unlikely that you'll ever get to see a correctly recorded EICR, they must be as rare as Hens Teeth from what i can make of it!! lol!!
 