, the rcd will still protect against this? Only problem being I can’t really test the theory out without an earth?

No, in this situation an RCD disconnects the circuit once a person is already receiving an electric shock. A 30mA RCD disconnects the supply before the shock reaches a level that is not normally fatal for a healthy adult.
 
No, in this situation an RCD disconnects the circuit once a person is already receiving an electric shock. A 30mA RCD disconnects the supply before the shock reaches a level that is not normally fatal for a healthy adult.
Maybe the 30ma will knock some sense into him. :D:D All jokes aside the metal faceplates definitely need to go
 
nursey just called, it's past my bedtime... boing, sed zebedee
 
If they don’t feel the need for any earth on the circuits why do they feel the need for a new fuse board

Might as well just leave everything alone and as it were...
That’s most definitely the sensible thing to do but I’m assuming it’s because A) the current board looks terrible and the fuseboard cover is not in the best condition and B) that in the very rare occasion the fuse blows , my dad has to replace the wire and he can’t be assed with it
 

Reply to Dual board with no earth on final circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock