I agree mate. Thanks for input. Board change will take place then and replace the lot with plastic regardless.
Replacing accessories or parts with plastic is not necessarily a resolution of the issue as these replacements would have to be deemed and identified as Class II. See Regulation 415.1.2
 
@Sparksaflyin . Well the supply may be eves fed to the terrace to supply alternate houses on different phases .
Usually the distribution is on an end gable , but I have seen them distributed from inside a property
 
Replacing accessories or parts with plastic is not necessarily a resolution of the issue as these replacements would have to be deemed and identified as Class II. See Regulation 415.1.2
Maybe that is the case but the regs usually advise to change what is “reasonably practicable” and If they won’t let me rewire then I can only make it as safe as possible without. If the screws are insulated, the fittings plastic and the circuit protected by an rcd then I think it will be extremely difficult for someone (even my father ) to receive an electric shock
 
Fitting plastic caps over the screw heads is totally ineffective in providing Class II insulation. Aside from that Class II light switches do not exist.
 
Well the supply may be eves fed to the terrace to supply alternate houses on different phases .
Usually the distribution is on an end gable , but I have seen them distributed from inside a property
Good shout! That would then make sense as to why it’s 3 separate armoureds coming in. Doesn’t make sense to me why they would all come into one property though?
 

Reply to Dual board with no earth on final circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
283
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
507
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
915
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock