I recently wired a new commercial kitchen, the kitchen had all new steel tables and commercial dishwasher. All circuits on RCBO's, all Zs readings well within limits, 1 week after the install someone calls to say there getting a shock off the dishwasher. When I get there I'm measuring 180v from the casing of the dishwasher!!
The company that supplied all the kitchen equipment said all the equipment should be separately earth bonded..
Which I knew they would say this as to get out of any blame, but surely the earth connection within the dishwasher should be adequate enough, and if its not then its a fault with the dishwasher?? Or is it that no manufacture can guarantee there earth in the appliance will work? So then tell the electrician "bond everything"
I think it's a cop out!
The company that supplied all the kitchen equipment said all the equipment should be separately earth bonded..
Which I knew they would say this as to get out of any blame, but surely the earth connection within the dishwasher should be adequate enough, and if its not then its a fault with the dishwasher?? Or is it that no manufacture can guarantee there earth in the appliance will work? So then tell the electrician "bond everything"