I recently wired a new commercial kitchen, the kitchen had all new steel tables and commercial dishwasher. All circuits on RCBO's, all Zs readings well within limits, 1 week after the install someone calls to say there getting a shock off the dishwasher. When I get there I'm measuring 180v from the casing of the dishwasher!!

The company that supplied all the kitchen equipment said all the equipment should be separately earth bonded..

Which I knew they would say this as to get out of any blame, but surely the earth connection within the dishwasher should be adequate enough, and if its not then its a fault with the dishwasher?? Or is it that no manufacture can guarantee there earth in the appliance will work? So then tell the electrician "bond everything"

I think it's a cop out!
 
TPES where was that 180 volts coming from, a fault on the dishwasher?

If it was an earth fault then why didn't the RCBO trip?

Was you picking up the 180 volt from case to neutral or case to table?

Think there should be a bit more investigation by the company rather than the get out of bond everything
 
I recently wired a new commercial kitchen, the kitchen had all new steel tables and commercial dishwasher. All circuits on RCBO's, all Zs readings well within limits, 1 week after the install someone calls to say there getting a shock off the dishwasher. When I get there I'm measuring 180v from the casing of the dishwasher!!

The company that supplied all the kitchen equipment said all the equipment should be separately earth bonded..

Which I knew they would say this as to get out of any blame, but surely the earth connection within the dishwasher should be adequate enough, and if its not then its a fault with the dishwasher?? Or is it that no manufacture can guarantee there earth in the appliance will work? So then tell the electrician "bond everything"

I think it's a cop out!

PAT the dishwasher. that'll tell you if it's faulty or not.
 
I've seen Catering equipment with separate earth lugs on the back recently.

And I previously worked on catering equipment for around 10years and never noticed in M.I's that this was the case.

It can't be C.E or B.S to have to have a fixed earth lead on portable equipment.
 