Hi

I have been to see a job that has a TT system installed for the house. Dual RCD board in the house. All up to date.
I am looking to use a spare way in the house consumer unit to run some power to the garage. If i use a 3core SWA (one of the cores being the earth), do i need to install an earth electrode for the garage or will running from the existing board be ok?

Appreciate any help.
cheers
 
Use the existing if its ok, just check if its a metal board its got the 100ma type s upfront instead of the main switch as its TT, I've come across a few that havnt.
 