steve100

If I am carrying out a Zs test on a final ring circuit in an installation, say as part of a periodic, is it okay just to turn the equipment off? Or should I disconnect them from the supply (turn the socket off)?

Also would the same principle apply when testing the RCD?

Thanks
Steve
 
By the time you've got do the Zs tests you should have already done the IR tests and every load should be already unplugged. But saying that, yes you can just switch off any load at the socket and with a plug in adapter to take you Zs readings at the sockets.
 
And I presume you would use the same approach when testing the RCD? If for arguments sake you did leave a load on while carrying out either the Zs or RCD test then would this give you a force reading as apposed to damaging any equipment or could it potentially damage equipment and give false reading?
 
Its always best to unplug any loads whilst testing, especially IR testing because electronics do not like 500V DC up em lol. Knew a chap that fried a Sky tv box few years ago by doing an IR whilst it was still plugged in, he had to buy the customer a new one.

As for the false readings? Dont think it would because the fault current of (lets say x 5) 150mA that your IR tester is sending down the circuit is going to cpc/earth and this will go via the lowest point of resistance to the MET at the cu. What you may get is earth leakage from loads on the circuit and therefore you mft or IR tester will show a lower mA that made the RCD trip.
 
I'd always unplug the equipment, I've been on the receiving end of a spurious claim from the tenant of a council house. Better safe than stupid.
 