Hi all,

Just wanted to let everyone that replied to my post that it is now solved! The problem was a faulty RCD. I got there this morning and ramped tested the RCD at the board with all the circuits switched off and got a reading of 15mA. I changed over the RCD, ramp test that and got 27mA :)
Got disconnection times of 28.8 x1 and 9.7 x5 and a Zs of 0.48. Obviously all appliances are staying on too, so customer can have washer and dishwasher running at the same time, all good!
Just a quick question - do you guys do a full installation test before you start any alterations? In hindsight this would probably spotted the problem before I started any work and I am now considering doing full testing before hand!
Thanks for your help on this subject everyone!

:)
 
This type of issues coming usually in the appliances so first switched off and also plugged off the appliances then do the RCD test it will show problem wherein appliances or earth leakage.
 
Last edited by a moderator:
Hi all,

Just wanted to let everyone that replied to my post that it is now solved! The problem was a faulty RCD. I got there this morning and ramped tested the RCD at the board with all the circuits switched off and got a reading of 15mA. I changed over the RCD, ramp test that and got 27mA :)
Got disconnection times of 28.8 x1 and 9.7 x5 and a Zs of 0.48. Obviously all appliances are staying on too, so customer can have washer and dishwasher running at the same time, all good!
Just a quick question - do you guys do a full installation test before you start any alterations? In hindsight this would probably spotted the problem before I started any work and I am now considering doing full testing before hand!
Thanks for your help on this subject everyone!

:)

So if everything was OK before you added these two extra sockets, then it was probably your IR testing that buggered the RCD then!!
By the way, the correct method of ''confirmation'' testing a RCD/RCBO is at the unit itself within the CU/DB, not downstream.
 