Hi folks,
installing back up gennys not my thing.Cant avoid this one though.Have looked through previous threads.Two things still not entirely clear for me are...

1) Are there any reasons why the homes existing earth electrode wont suffice?

2) If a separate rod is required ,what would be the recommended max. resistance?

Thx in advance
 
If the property has its own earth, it is likely to be sufficient.
you can’t rely on the suppliers earth, as it may well be disconnected during a power cut.
 
The requirements are for both the set to be grounded, and for that grounding to be carried over into the installation's MET. Therefore, if the property installation is already a TT with its own rod, then assuming that rod is actually fit for purpose with a respectable Ra then it can almost certainly be used. That being said, you need to pay attention to your isolation/switchover between one energy source and the other.
 
Thx guys.What would you regard as a "respectable Ra"?
This is where things can get interesting! Conventional wisdom says that anything over 200Ω isn't really worth much, despite the magical max number of 1667, hence why you need upfront RCD protection (again, conventionally either 100mA 's' type or by individual RCBO's). However.... the genset itself may well have a 'standard' 30mA RCD / 16 or 32A MCB (you don't mention the size of the set so I'm assuming small domestic / builders style) so that then gives you difficulties with discrimination. However (part B..) if you change that upfront OCPD to be something more suitable (say a 300mA 1s device) then you might fall foul of the need to protect the feed cable from the set to the property at 30mA unless you're prepared to accept that you'll be running out SWA, eg.

Whilst we're at it.... if it IS a smaller set then you'll need to refer to manufacturers info re the nature of it's Earth as it's most likely 'floating' and you'll need to create a PEN link at the set as well.
 
This is where things can get interesting!
Interesting!!well that about sums up the project so far.

Genset is a "Pramac p6000".
The owner got no instruction manual.
The dealer has not responded to my emails (3 in total) since 20/12/22.
The Pramac website does not currently have a technical helpline.Its "under maintenance".
Pramac utube videos are general information,not technical.
The manuals I,ve accessed so far had little to nothing in the way of specific guidance on earthing arrangements.
The only specific info I found was on their main site.It stated regarding pramac portable generators that "do not need to be grounded"?? No further explanation given.

Make of that what you will.
I,ll be back.
 

Reply to Earth rod for back up genny in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
482
Like a host of UK residents recently (230% increase in genny sales apparently), I've just invested in a small (3500W) portable, dual fuel...
Replies
12
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I was away at the weekend & the electrician came round to fix something. While there he decided to condemn an outdoor electrical light as he said...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock