Cookie the panel is probably 200 amps and the wire size should be 2/0 copper. Aluminum wiring would be 4/0 aluminum. We install 2 ground rods regardless of the resistance to ground. I have never read 25 ohms from the panel to the rod. It’s always less than 1 ohm. The # 6 wire is correct and if the conduit is metal yes it has to be bonded to the panel by means of a grounding bushing
Hi Megawatt. Am curious about your comment that you "never read 25 ohms from the panel to the rod. It's always less than 1 ohm".
2 questions
1) Does that means that YOU take fault loop impedence tests even though as Cookie mentioned earlier you are not obliged to do that if you have sunk 2 rods?
2) Am I correct to conclude that you always get a reading of less than one ohm every time you sink 2 rods? ie you have never had a situation where you found it necessary to sink a third rod in order to achieve a reading of less than 1 ohm?
 
Hi Megawatt. Am curious about your comment that you "never read 25 ohms from the panel to the rod. It's always less than 1 ohm".
2 questions
1) Does that means that YOU take fault loop impedence tests even though as Cookie mentioned earlier you are not obliged to do that if you have sunk 2 rods?
2) Am I correct to conclude that you always get a reading of less than one ohm every time you sink 2 rods? ie you have never had a situation where you found it necessary to sink a third rod in order to achieve a reading of less than 1 ohm?

Read his post again, he has never had a reading over 1ohm from panel to rod, that's the resistance of the copper or aluminium conductor between the panel and the rod. He's not talking about the rod's resistance to Earth.
 
  • Agree
Reactions: DPG
Read his post again, he has never had a reading over 1ohm from panel to rod, that's the resistance of the copper or aluminium conductor between the panel and the rod. He's not talking about the rod's resistance to Earth.
?
It is commonly seen in lighting protection guides. Not quite sure why that specific value though. For example, page 57 of this document:
Good read that. Thanks for posting it.
 
  • Like
Reactions: pc1966 and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Earth Rods in TN-C-S and TN-S
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
Cookie,
Last reply from
LastManOnline,
Replies
43
Views
15,371

Advert