Hi Megawatt. Am curious about your comment that you "never read 25 ohms from the panel to the rod. It's always less than 1 ohm".Cookie the panel is probably 200 amps and the wire size should be 2/0 copper. Aluminum wiring would be 4/0 aluminum. We install 2 ground rods regardless of the resistance to ground. I have never read 25 ohms from the panel to the rod. It’s always less than 1 ohm. The # 6 wire is correct and if the conduit is metal yes it has to be bonded to the panel by means of a grounding bushing
2 questions
1) Does that means that YOU take fault loop impedence tests even though as Cookie mentioned earlier you are not obliged to do that if you have sunk 2 rods?
2) Am I correct to conclude that you always get a reading of less than one ohm every time you sink 2 rods? ie you have never had a situation where you found it necessary to sink a third rod in order to achieve a reading of less than 1 ohm?