Hi - My first post to this forum.

I am having a disagreement with another electrician on the type of the supply characteristics for a domestic installation, i.e. whether it is TN-S or TN-C-S. I have uploaded a photo of the cutout/supply head. To resolve the disagreement I suggested we ask for a 3rd, 4th, 5th .... opinion from the forum.

The building is in a suburban area and is over 100 years old , not that I am suggesting that the supply head is that old. There are no PME labels/markings. The measured Ze is 0.11 ohms.

Thanks for your views in advance.

jlrb

Supply Type.jpg
 
only DNO could tell you for sure . rare to see supply in split concentric.
 
measure both pefc and pscc. if they are the same, i'd opt for TNC-S.
 
you could always dig up the supply cable and see where the earth is. :(
 
Did you test L-N fault loop?

measure both pefc and pscc. if they are the same, i'd opt for TNC-S.

As Murdoch and telectrix suggested:

Measured PEFC = 2.10 kA (0.11 ohms)
Measured PSSC = 1.30 kA (0.18 ohms)

This indicates to me that it is TN-S rather than TN-C-S, but I was expecting the relative values to be the other way around - but on reflection I am not sure why I should expect that.
 
Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?
 

Reply to Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
735
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock