GLENNSPARK
we get this quite a bit with the letting agents we do some work for....no CPCs in lighting cables.....the cables you give a 4...as long as continuity and IR are good......the knockout box would classify as an exposed conductive part if as has been mentioned above..its of the type with metal lugs for the screws and the screws themselves are metal....so again as above either plastic screws and/or screwcovers...sorts it and a note as to the absense of a CPC within the lighting cable....watch for class 1s in situations like this.....some of the tennants in the lets we service have a habit of doing diy retrofits of lighting they have bought (more often than not class 1s)....if i see em i ALWAYS check to see its compliant.....wont hesitate to drop em if theres no cpc present......