you cannot use the adiabatic equation for a TNCS(PME) main earth as this is sized according to the suppliers neutral conductorr

Not wishing to sound like a pedant, but it is actually the main bonding conductors on a PME system that are sized in accordance with the suppliers neutral. The main earth then has to meet the requirements for the main bonding conductors :D
 
No this is not quite right

you can use table selection sizes or adiabatic equation for TNS/TT main earths

then as per regs the bonding conductors must be no less than half that of the MINIMUM required earthing conductor(through calculation or selection methods) AND not less than 6MM

thats why there are such skinny little earth tails soldered onto TNS cable sheaths by the DNO

you cannot use the adiabatic equation for a TNCS(PME) main earth as this is sized according to the suppliers neutral conductor, in the event of a lost supply neutral the main earthing and bonding conductors will potentially be carrying network current and must be considerably larger

well put, i couldnt be arsed to type that lot out
 
This subject has cropped up on here a few times and myself included has misinterpreted the regs wrong to be corrected thankfully by other forum users. I have come across numerous situations where a basement intake on a PME system has served separate flats wired in 16mm/4mm2 T&E cable upto a board located in each flat. Sometimes the actual main gas and water are located within each flat and have been bonded using 10mm2 back to the board but then rely on the 4mm2 earth as a combined earthing and bonding conductor back to the intake position. The nightmare is then having to upgrade the main earth to 16mm2 to accommodate the correct size bonding. Sometimes this could be a very long and awkward run and involve extensive damage to decor!!
 
In which case if any works was undertaken in those flats then the main earth would have to be upgraded.
 
Yep you're spot on problem is trying to explain this to the local authority who payed the idiots to incorrectly provide bonding to the incoming services in the first place!!
 