So what your saying welch boy is you can use adiabatic formula for tns but not tncs is that right
yep thats right
So what your saying welch boy is you can use adiabatic formula for tns but not tncs is that right
you cannot use the adiabatic equation for a TNCS(PME) main earth as this is sized according to the suppliers neutral conductorr

No this is not quite right
you can use table selection sizes or adiabatic equation for TNS/TT main earths
then as per regs the bonding conductors must be no less than half that of the MINIMUM required earthing conductor(through calculation or selection methods) AND not less than 6MM
thats why there are such skinny little earth tails soldered onto TNS cable sheaths by the DNO
you cannot use the adiabatic equation for a TNCS(PME) main earth as this is sized according to the suppliers neutral conductor, in the event of a lost supply neutral the main earthing and bonding conductors will potentially be carrying network current and must be considerably larger