I am doing some wiring in Southern Spain. I discovery that blue wires can be live here-thought I share this one with you all! Based on the age of many installations some dating more than 30 years, many electrical installations don’t have an earth system in the installation. The fuse box, also old doesn’t have earth terminals.
In view of this, I am contemplating wiring in an earth wire through the conduit and linking it to together at the main incoming service breaker panel. Rational; it is upstream from all fuses and or circuit protecting the hot wires from various circuit installations in the building.
The final end of earth conduct would be fastened to anything conductive, i.e copper lamp hook on ceiling lights and copper part in sockets.

Is my method sound?
 
I do not know the Spanish regulations but from a UK perspective, if you are just supplying a cable to all the fixtures from a linking connection in the main breaker panel without having a means of earthing for the installation then you are providing no safety, possibly decreasing safety.

There has to be a means of earthing that can provide the safe route for current to flow so that the circuit protection device can operate.
In the UK if there were no means of earthing provided by the network then the installation would need to be fitted with an earth rod /tape / plate that would provide an earth for the installation as a terra terra system, residual current device protection would also be required if the earth loop impedance was not low enough to operate a circuit breaker.
 
Is my method sound?

Well if you need to ask the question, you really shouldn't be touching anything electrical in Spain, or anywhere else!! For God's Sake, hire an electrician you obviously have no idea what you're doing!!
 
We can't possibly comment on an installation in spain, we follow BS7671 (British Standards) so even with an indepth knowledge of the BS7671 how can we really make a judgement of an installation subject to spanish regulation?
 
I have dabbled a bit with Spanish ‘electrikery’ and their system is very similar to the UK regs. To try and assist the OP my limited “understanding” of Spanish regs is …..

Your “Blue” wire is live because the Spanish do not have a requirement for ‘polarity’ in their regs. You can interchange the Live and Neutral so the Brown or Blue wire can be live. Beware when working on cabling! Also the Spanish still allow Red/Black cable to be used so beware of colours.

I take it you are in a rural area where normally there will be no “earth” provision from the supply network. The Spanish regs require you have an earth provision the same as in the UK and the method you are suggesting would be totally unacceptable and I believe unsafe. If not supply provided you need to provide an earth which is usually achieved with an earth rod(s). Due to the warm ground conditions in Spain, plus the rocky/rubbly ground, it can be very difficult to achieve an acceptable level. (Lots of info on this site regarding earth rods if you search). This is required for amongst other things the fact that Spanish regs require all circuits to be RCD protected and without an acceptable earth value the RCD wont function.

Im guessing you have an old Spanish electrical installation which looks like it doesn’t meet any of the regs I have allude to above and probably doesn’t have a ‘Bolletin’ to prove conformance to anything? I would seriously recommend you get a Spanish registered electrician in to sort out your earthing issue which from what you are describing will probably require a new fuseboard fitting. They can then issue a Bolletin to prove conformance to regs. The electrical supply networks are supposed to ensure all properties have a valid Bolletin and can disconnect you if you don’t have one – they certainly wont connect you to the network without one!

Finally, I believe the Spanish government are steadily clamping down on un-registered electrical workers so if you use an un-registered electrician not only will the un-registered electrician get fined but you will be fined too. (Wouldnt this be a novel experience for the UK!!)

CAVEAT : I stand to be corrected on any of the above by knowledgeable Spanish ‘sparkies’ …..
 
Thanks for those of you who posted useful comments.
I understand the rationale of earth wiring to provide an escape path in the event of leakage in the circuitry, thereby avoiding electricity flowing through human body, since electricity finds the path of least resistance, for it to be effective in providing safety against electrocutions the earth conducts have to provide less resistance than the human body. According to the regulations earth resistance should be less than 1 ohm.
In an ideal world changing the fuse box with earth terminals would be best. But the issue here is money-many customers are having difficulty just buying food and keeping light on- this is the reality!
Let me explain my method- the earth conduct would be linked to the NUETRAL wire at the main incommoding service panel the end. It is upstream from all fuses and or circuit protecting the hot wires from various circuit installations in the building. The installation would be fitted with and RCD. The final end of earth conduct would be fastened to anything conductive, i.e copper lamp hook on ceiling lights and copper part in sockets.
I have simulated this system in a safe environment, deliberately created a short circuit, used defective appliances and the RCD trips, no escape of electricity.
Waiting for intelligent comments/ criticisms.
Thanks
 
Without wanting to sound condescending, its probably best that you do some research youself as to why in the UK what you are proposing of linking the Neutral is "acceptable" when done by the supply company (DNO) to produce a TN-C-S system but would not be acceptable in Spain.

Spanish regs (REBT) require that you have a TT system installed if no "earth" is supplied by the likes of ENDESA (e.g. an earth rod) for a good reason. Think around how in the UK they ensure the neutral is always earthed throughout its run (PME) but the Spanish system isnt, and the implictions of what you are proposing in Spain on electrical safety in the instance of a fault current should "earthing" not be present. (From your own home and others! )

If you can understand that then you will have answered your own question as to why you shouldnt do what you are proposing. If you cant then Im sure a competent Spanish electrician will be able to advise you as to the rationale of why.

I have family living in Spain so appreciate the financial implications in the current environment but please seek professional advice on what you propose to do!
 
All counties have regs, if you don't know what they are, find out before you do anything. I would not wire anything here in France on the basis of UK regs as they are different from those here, as they are in Spain, Germany etc. Try looking on the internet for Spanish regs, you will find its all there.

Sorry to have a moan, but it sounds from you posting that you have no idea of what you are doing with regards to Spanish wiring.
 
Thank you for that. So having local knowledge of the supply distributor is needed. Referring to the TN C-S system earthing the distributor would need to provide a main earthing terminal, which is linked to the incoming neutral terminal. If this configuration is not provided by the local distributor then a TN C-S system can’t be implemented by the local electrician.
I am collaborating with the longest established local Spanish Electrical Service company in my area. During the boom period this guy had 50 vans and electricians working for him-he is now down to 8!
Anyway, local knowledge of supply distributor is invaluable. Last week I visited a business that had spent a small fortune on neon lights. After two years his neon lights no longer worked. 240 V was going into the transformer, but no electricity circulating to the neon lights. My local contact said that power distribution in our area is irregular, jumps etc, which damages transformers….
So what have I learnt-local knowledge of supply distributor is needed before recommending solutions that customer’s will be happy with.
 
What you should have learnt, ...is that you DON'T touch electrical installations past changing a plug top!! What the hell are you doing playing around with electrical installations that you clearly have little to no understanding. You are nowhere close to being competent as to advise customers on any solutions involving electrical installations, ...end of!!

You sound like a jobbing Do It All builder/handyman or something, you're certainly not an electrician. So get the local guy with the 8 vans to do any electrical work that comes your way....

And if you don't take this as '' intelligent comments/ criticisms'' then more fool YOU!!
 
No need to waste my time with such an idiotic comment!
Already rectifying problems of other electricians, by the way I am also qualified.
If this forum is turning into a bashing session-then frankly it is a waste of time!
You sound like a little wimp, who is trying to make himself sound big in the shadow of an anonymous forum. In reality you have probably never held a screw driver in your hand-let alone worked on electrics!
 