This has probably been asked before.
Can anyone explain to me why the maximum EFLI on a TT system to operate a 30mA RCD in the required time (table 41.5) is 1667ohms yet on a TN system, depending on the device rating ,table 41.3 is max of 15.33ohms (Type B 3A rating) I am aware of NOTE 2 200ohm
 
The 30ma device which is quoted as 1667 ohms is a 61008 and does not have over current protection. The 60898 and 61009 both have over current protection and hence require a lower Zs reading to operate in the time scales given in the tables.

Hope this helps.

BillR3
 

Reply to EFLI on TT systems in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock