Hi all new to form so thought I would as a question.
Testing a final ring circuit & all is normal apart from the live / brown legs of the circuit which are too short to reach the MCB so they have connected them together in a block & extended it within the CU via a 6mm to the MCB
Just wondering how you would code that if at all?
 

Attachments

  • 20220201_102157.jpg
    20220201_102157.jpg
    690.3 KB · Views: 18
Ideally they should be extended separately with the same size cable as rest of circuit…
I might C3.
doesn’t have to be changed, but would save confusion when the schedule of test results says 2.5, but it’s 6mm leaving the breaker.
 