Just doing some mock exams for the upcoming 2391 course.

Confused on this question as I got it wrong.

Q. If a lighting circuit installed in metal conduit in a shop supplied from a TNS system had no RCD provided for fault protection but achieved disconnection times what would the outcome be on the schedule of inspections.

I put it as a C3. Improveme needed.

The answer has come back as N/A.

Can any explain this?
 
Yes the question is a bit confusing its trying to dissect what they are getting out , For example what part of the schedule are they referring to

RCD(s) provided for additional protection, where required - includes RCBOs (411.3.3; 415.1) then N/A

Adequacy of protective devices: type and rated current for fault protection (411.3) then it would be Pass​
 
Doesn’t matter if it’s earthed.
Doesn’t matter if it’s surface or concealed.
Only thing that would mean RCD protection is required, is if it’s part of a circuit of a location containing a bath or shower.
It’s a shop, so that is unlikely.
I thought if your using conduit as mechanical protection it had to be earthed , or does it not because conduit will prevent a screw or nail from Penetration , ( Now there a word for a Friday afternoon :))
 
I thought if your using conduit as mechanical protection it had to be earthed , or does it not because conduit will prevent a screw or nail from Penetration , ( Now there a word for a Friday afternoon :))
The options for providing additional protection for cables concealed in walls are:
to bury the cables at a depth greater than 50mm,
to use a cable with an earthed screen,
to use earthed conduit or trunking,
to provide mechanical protection sufficient to prevent penetration by screws and nails,
to run the cables in prescribed routes and provide RCD protection.
 
The options for providing additional protection for cables concealed in walls are:
to bury the cables at a depth greater than 50mm,
to use a cable with an earthed screen,
to use earthed conduit or trunking,
to provide mechanical protection sufficient to prevent penetration by screws and nails,
to run the cables in prescribed routes and provide RCD protection.
Ok so it has to in an EARTHED conduit system. So conduit must be EARHED
Unless the conduit is sufficient to protection to prevent penestration by screw or nail. Then NO EARTH is required.
Now I would of said that all the metal conduit I have used would stop a screw or nail but is there any metal conduit that could be penertrated?