Arms
r2 on a RFC, not continuous, but every socket has an earth & acceptable Zs. Code 2 or 3 (r1 & rn are fine)?:dunce2:
 
C3 in my book, unless the pefc is abnormally high.
 
Use the adiabatic equation to confirm whether or not the single cpc size is adequate. If so, no code, but noted. If not, C2.
i agree. if the single cpc can withstand the pefc, then a C3.
 
Why a C3? We run ring final circuits in steel conduit and use that as a single earth.

Where is the reg that says r2 must be a ring?
 
C3... improvement recommended. i'd be inclined to fix it if it could be done economically and without pulling up floors etc.
 
Why a C3? We run ring final circuits in steel conduit and use that as a single earth.

Where is the reg that says r2 must be a ring?

Reg 543.2.9 says that with the exception of metal enclosures or coverings used as a cpc the cpc must be run as a ring with both ends connected to the earthing terminal at the circuits origin
 