I had an EICR done the other day to update the old one which was a pass/satisfactory. The new EICR has failed although nothing has changed no alterations/additions absolutely nothing. The flat is in a block of 150 flats which were built in 2006.

Please could somebody advise as to why it has failed this time the reasons given are in the first attachment but essentially:
1. bathroom lights are not RCD protected (I think they are there is only one lighting circuit !!)
2. Breakers need to be respected because of buzz bar

I am attaching a screenshot of the failures and also pics of the Consumer Unit which states on the front cover that all circuits are RCD protected !!

I'd be very grateful for any advice, I can't understand how the installation passed 5 years ago but doesn't now !!
Thank you once again for your assistance.
 

Attachments

  • Puzzled.png
    Puzzled.png
    374.4 KB · Views: 45
  • Consumer unit Cover.jpeg
    Consumer unit Cover.jpeg
    2.1 MB · Views: 43
  • List of circuits.jpeg
    List of circuits.jpeg
    2.2 MB · Views: 42
  • Inside consumer unit.jpeg
    Inside consumer unit.jpeg
    2.2 MB · Views: 45
I have absolutely no idea what item 3 stands for apart from being grammatically incorrect, buzzbar should be busbar, I am clueless. Are you confident enough to remove the cover and take a picture but switch it off first.
 
Dear Westward
Thank you for replying so quickly, I'll get the picture for you but it won't be until later this evening I'm afraid as I'm not there at the moment.
Thank you so much for your interest.
Warm regards
Paul
 
The board is split…. Ie, left hand side is on mainswitch… right hand side on rcd… so there should be 2 busbars..
if there’s only 1, then the rcd has been functionally bypassed.
Can you post up the schedule of test results / circuit chart page of the EICR showing RCD trip times

As Westy suggests, take the cover off (isolate the entire board first) and take a photo




The regulation about lighting on an rcd is fairly new, and may not have been in place at the time of the previous report, but even so, it should only get a C3, as long as it was within regs at the time of installation.
 
The board is split…. Ie, left hand side is on mainswitch… right hand side on rcd… so there should be 2 busbars..
if there’s only 1, then the rcd has been functionally bypassed.
Can you post up the schedule of test results / circuit chart page of the EICR showing RCD trip times

As Westy suggests, take the cover off (isolate the entire board first) and take a photo




The regulation about lighting on an rcd is fairly new, and may not have been in place at the time of the previous report, but even so, it should only get a C3, as long as it was within regs at the time of installation.

Thank you Littlespark for your update.

I use a company that allocates EICR testers and to add potential insult to potential injury I just realized that the person who passed it 5 years ago is the same person who failed it this time !!

I am attaching the outcomes from the report 5 years ago and the redacted report that I received today.

Many thanks for all your assistance.
 

Attachments

Just the very fact they use the term buzzbar makes me wary.
The bathroom RCD issue was Code 3 previously and if nothing has changed that should still be the case so I would be questioning this.
They failed to comment on the type AC RCD and the plastic consumer unit.
I would also question the meaning of item 3 and why it wasn't noted previously.
 
looks like it was filled in in a hurry...
A couple of things after a quick look.

They have filled in RCD details for every circuit, where only the last 3 i believe are RCD protected.
They haven't filled in the BS/EN for the RCD which is likely 61008...
A circuit there i think is labelled kitchen appliances ring.... which should be RCD protected like all the other sockets.
Mixed up the values between the Amp rating of the RCD (80A) and the tripping current (30mA) That's just careless.

As mentioned... the C2's have been too strict, and item 3 really doesn't make sense without a look inside the CU. Any faults listed should be backed up by a reg number, or explained in such a way that anyone can understand
 
looks like it was filled in in a hurry...
A couple of things after a quick look.

They have filled in RCD details for every circuit, where only the last 3 i believe are RCD protected.
They haven't filled in the BS/EN for the RCD which is likely 61008...
A circuit there i think is labelled kitchen appliances ring.... which should be RCD protected like all the other sockets.
Mixed up the values between the Amp rating of the RCD (80A) and the tripping current (30mA) That's just careless.

As mentioned... the C2's have been too strict, and item 3 really doesn't make sense without a look inside the CU. Any faults listed should be backed up by a reg number, or explained in such a way that anyone can understand
Many thanks to both Westward and Littlespark !!!
I'll get in touch with the testers and see if they can explain further but thank you both very much for your expert insight and observations.
This electrical stuff is tricky isn't it ? Thank goodness this forum exists without it I'd be stuck !!
:) Warm regards, Paul
 
Well that could have gone better !!!
I spoke briefly to the electrician this morning(obviously WITHOUT mentioning this forum) and apart from being grumpy he was adamant that the flat was a FAIL because of no rcd on bathroom lights. He sent me some images via WhatsApp and confirmed the fail by WhatsApp.
I've responded politely by stating that I will send him a more detailed email.
Would you mind just checking my homework please ?
I looked up the regulations governing my flat and since it was built in 2006 it should be governed by the 16th Edition.
From my research the RCD protection for bathroom circuits came in under the 17th edition which was implemented from mid 2008.
The regulations are NOT retrospective and therefore the requirement for a RCD protection is not a reason to fail and should be C3 and not C2 which the same electrician had placed on the report 5 years ago.

I'm not sure whether he was being grumpy and helpful by sending me the images (attached) but aren't the readings immaterial if the regs don't cover it ? I may of course be the chump here and missing something so any comments on the images would be gratefully received - especially the BUZZ BAR C2 which nobody could understand earlier. Its not clear what the readings relate to, but one was definitely taken in the kitchen.
Thanks once again, this looks like an uphill struggle but I promise not to trouble you any further !!!
Warm regards
Paul
 

Attachments

  • Kitchen reading.jpg
    Kitchen reading.jpg
    128 KB · Views: 31
  • 494. 0.47 reading .jpg
    494. 0.47 reading .jpg
    152 KB · Views: 20
  • 0. 751 reading.jpg
    0. 751 reading.jpg
    167.3 KB · Views: 19
  • Cover off Consumer unit.jpg
    Cover off Consumer unit.jpg
    138.9 KB · Views: 21
  • Consumer unit .jpg
    Consumer unit .jpg
    181.7 KB · Views: 23
  • bus bar.jpg
    bus bar.jpg
    182.8 KB · Views: 26
Most of those readings in the images mean absolutely nothing (two are RCD tripping times) without further context.
Whilst the installation fell under the 16th Ed you still test it to current Regulations.
The statement in the original Report regarding the RCD for the bathroom providing the supplementary bonding is still in situ is the statement which should be in your new Report as a C3.
Could do with a clearer internal picture of the consumer unit, one is blurred and the other his lead clips are in the way although it does look normal.
 
Thank you Westward your assistance is very much appreciated.
I promise not to continue this thread - but I will post the outcome at a later date.
Many thanks once again, this forum is amazing and the time and knowledge that you are willing to provide is exceptional !! Consider my faith in electricians restored !!
All the best.
Warm regards, Paul
 
Thank you Westward your assistance is very much appreciated.
I promise not to continue this thread - but I will post the outcome at a later date.
Many thanks once again, this forum is amazing and the time and knowledge that you are willing to provide is exceptional !! Consider my faith in electricians restored !!
All the best.
Warm regards, Paul

Most of those readings in the images mean absolutely nothing (two are RCD tripping times) without further context.
Whilst the installation fell under the 16th Ed you still test it to current Regulations.
The statement in the original Report regarding the RCD for the bathroom providing the supplementary bonding is still in situ is the statement which should be in your new Report as a C3.
Could do with a clearer internal picture of the consumer unit, one is blurred and the other his lead clips are in the way although it does look normal.
Dear Westward,
I just wanted to say a big thank to you for all your skill and knowledge - I finally received my updated EICR yesterday. Without your invaluable assistance I'm sure it would have been an even greater faff !! Thank you once again Paul
 