yea, but ring is one circuit not 2 radials.
and yes, i have failed, and i thought it was not fair then, but now it does make sense to me.
Or maybe life is just unfair for Di's, ... on one assessment i had no grommet on first socket i was asked to open, explained my self to the guy, builders moved socket without my knowledge slightly to the right, client confirmed that on site.. spend 2 hours showing every possible connection then.
Inspector was satisfied, but in his report included missing grommet, and i was turned down by head office, not the inspector, because of silly builder.

2 Radials, in one MCB is one circuit, not 2 circuits.
 
2 cables connected into 1 MCB is still 1 Circuit though, not a cat in hells chance you failed a NIC assessment for that. Every ring main has 2 conductors in 1 MCB
[automerge]1594042621[/automerge]
And getting into a chamber to swap 100A fuses for 200A ain’t something anyone could do.
not impossible...especially that 200A MS is clearly visible! its what i learned a while ago, protect yourself from stupidity of other people.
it is no code probably, but as inexperienced in eicr im asking for advise, right?
 
Ok, the 200A Main switch is irrelevant, there are loads, and I mean loads of three phase boards with 125A Main Switches on 100A Incomers What type of fuses are currently in place, is it a standard 3 phase cutout or is it in a fuse chamber?
 
Ok.
Go through them and assign a reg number to each item that it doesn’t comply with. Then in your opinion do you find it to be a C1, C2 or C3?
I’ll give you some feedback when I see what your thinking behind them all is ?



Every single consumer unit have big cable entry hole behind, you can see cavity behing, cons units very dusty inside cause of that, im guessing wind blows , needs to be sealed.....
527.1.1 and 527.2.1 c2 or c3


subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded
522.8.5 c2


Consumer units are 2 rcd split boards, plastic, positioned right by the entry doors, inside every flat, i would recommend to replace them for metal, but .... do i code it as c3? -
421.1.201 c3 as located right be the only entrance doors without any enclosure




Every kitchenette appliance is integrated and have isolator above worktop except Microwaves, they are also integrated on a plug behind...
No code, 13a plug behind


kitchenettes are very small, hence all of the sockets and appliances isolators above worktops are either above sinks, or within 300 from induction hobs or sinks.
512.2 no code as no water or heat damage.. just reconfirmed its 100mm from hob


And finally landlors supply... all external lights permanently on, no sensor or switch, just an mcb.. there used to be a switch but blanked off... code?
537.3.1 no functional switching c3, also part l br, as on all the time.


there is 3 phase consumer unit with 40a mcb's to supply each flat, main switch on that board is rated 200a, same as meter, is rated 200a, but main fuses are 100a, but cores from the street looks like 35mm or even bigger. Meter tails installed are 25mm. I would do the tails to match 200a board capacity, right?
no code


meter tails terminated to 200a main switch, actually one, l3 looks black/dirty, not sure its burn, or just dirty, same behind the switch, on enclosure, it may be dirty, but couldn't confirm is, as whole building needed to be switched off, for which i had no permit.. would you code it?
suspected cable incorrect termination. No obvious damage, needs investigation f1

3 ph board not closing properly, i could see that is resting mostly on msbs, as they were not properly installed.. is that a code?? in same board there is a cover that covers l1 l2 l3 terminals after main switch, and is broken, cracked, attached to main switch with insulation take.... is that a code?
134.1.1 c3 as no immediate danger...
[automerge]1594050018[/automerge]
Ok, the 200A Main switch is irrelevant, there are loads, and I mean loads of three phase boards with 125A Main Switches on 100A Incomers What type of fuses are currently in place, is it a standard 3 phase cutout or is it in a fuse chamber?

Just one board, with 40a type b mcbs for each flat.
Original electrical installation certificate is written as one installation.

From 40a mcbs to single phase meters, from meters to flats.
 
More worrying that a DI is doing commercial work ? NICEIC allow DI to pay more and be assessed for EICRs. It’s a new thing for England PRS changes. With that many questions and the content of the. I’d query if the op is qualified and competent to do the EICR ?
 
Sorted.
Ive subcontracted eicrs to another company. £90 per flat. Niceic approoved contractors. Happy!
Ill do the remedial works
Let see what they will say.
 
can somene please comment on this swa please. I wuldnt do it that way,but need t know if you will find it on yur eir, will you pass it? third core is used as cpc, and armour earthed on the other side20200702_092010.jpg20200702_092010.jpg
 

Attachments

  • 20200702_091935.jpg
    20200702_091935.jpg
    97.1 KB · Views: 102
its what i would do, match tails to the MS, not to the fuse. Fuse can be replaced for a bigger one by anyone, all kind of maintenance people have access.

you got it wrong, it was a comment only, my issue was 2 radials on one mcb, not EL on lighting circuit.

That's nonsense, you size cables according to the OCPD rating, not the highest rated switch in a circuit!

2 conductors in one MCB is perfectly acceptable, and is still only one circuit.
[automerge]1594059693[/automerge]
More worrying that a DI is doing commercial work ?

I know, it's absolutely shocking isn't it.

I'll have to stop doing all of the commercial and specialist work I do and get back to domestic work since I am after all 'only a DI'
 
I have not even got domestic installer, doesn't mean I could not do the work, just that i can't self certify.
therefore i will stick to the easier stuff that requires no silly registration.
like 3 phase motors and controls!!
 
subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded 522.8.5 c2

How do you know it's not supported correctly? It could be.
As the armour is not being used as the protective conductor as long as one end of the armour is properly glanded and earthed it's ok (but not what I would do either).
 
there any requirement to fill any gap between the cables and the edge of the qu
subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded 522.8.5 c2

How do you know it's not supported correctly? It could be.
As the armour is not being used as the protective conductor as long as one end of the armour is properly glanded and earthed it's ok (but not what I would do either).
Thank you! what will you say about big hole behind CU to cavity wall? Cavity plasterboard on timber.
 
I have not even got domestic installer, doesn't mean I could not do the work, just that i can't self certify.
therefore i will stick to the easier stuff that requires no silly registration.
like 3 phase motors and controls!!
I’ll help ya out mate ??
 
not impossible...especially that 200A MS is clearly visible! its what i learned a while ago, protect yourself from stupidity of other people.
it is no code probably, but as inexperienced in eicr im asking for advise, right?

So your saying that becuase the main switch is 200A someone might replace 100A fuses with 200A fuses?
If they are going to do that then how do you know they would fit 200A fuses and not 300A or 400A? Maybe you should size everything for a nice round 1000A just in case?

My point here is that trying to 'protect yourself against the stupidity of other people' is impossible and quite pointless.

If someone is going to come along in the future and replace a fuse with one of twice its rating then they aren't going to worry about what is written on any switchgear before they do it!

Sometimes I install a 20A DP switch to isolate external lights on a normal 6A lighting circuit, but I sure as he'll don't wire the whole circuit in 2.5 just because there's a switch rated at 20A in the circuit!
 
So your saying that becuase the main switch is 200A someone might replace 100A fuses with 200A fuses?
If they are going to do that then how do you know they would fit 200A fuses and not 300A or 400A? Maybe you should size everything for a nice round 1000A just in case?

My point here is that trying to 'protect yourself against the stupidity of other people' is impossible and quite pointless.

If someone is going to come along in the future and replace a fuse with one of twice its rating then they aren't going to worry about what is written on any switchgear before they do it!

Sometimes I install a 20A DP switch to isolate external lights on a normal 6A lighting circuit, but I sure as he'll don't wire the whole circuit in 2.5 just because there's a switch rated at 20A in the circuit!
im not trying to argue with you, and im not asking it it is ok for me to do it, i just do it, and you dont have to agree with it.
and why would someone install 300a fuse if ON THE BOARD SAYS 200A Max.
But HEJ, even if they do im covered, as my TAILS and MS is 200A rated max! (load also matters)

And there is a difference between 20a and 100a in terms of harm it can cause, bad example.
 