I'm looking to install a new electric hob in replacement of my gas hob (I would have the gas hob professionally removed). I have an extractor hood and fan that I currently do not use this is hardwired into a socket on the wall, would it be possible to use this to wire up my new electric hob.
 
Hi Mark - we would need to know what was the new hob and also the size of the circuit breaker that the fan is on. You never know, but it's unlikely sorry.
 
Hi Mark . The hob needs its own supply back to the fuse board .Get a sparky in to have a look he may be able to find an unused existing supply.
 
I'm looking to install a new electric hob in replacement of my gas hob (I would have the gas hob professionally removed). I have an extractor hood and fan that I currently do not use this is hardwired into a socket on the wall, would it be possible to use this to wire up my new electric hob.

Mark

You can get some electric hobs where you can set them to either 13amp, 16 amps, 20amps etc (some of the high end NEFF induction hobs do this)
If your existing oven has its own 32amp supply this may be possible to add the hob to that circuit.
Get a local sparks to advise and quote
 
Mark

If your existing oven has its own 32amp supply this may be possible to add the hob to that circuit.
Get a local sparks to advise and quote

I do believe that my oven is wired into its own 32amp socket the oven I'm looking at says it's 13amp but the hob doesn't give an amps figure (it's a logik lchobtc16 ceramic hob if that helps) would that be safe to use them both on
 
applying diverssity, i's say it was OK to connect both oven and hob to existing 32A supply. been a rule of thumb for donkeys that 32A supply will handle a total stated max. load of up to 15kW.
 
Thanks for your help can I ask what is ment by diversity
diversity is making allowance for the fact that all elements will not be on together. i.e. they switch on/off with their thermostats, soeven thogh the full load may be 40A, diversity would bring this down to around 20A -22A.
 

Reply to Electric Hob installation in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock