Hi everyone!!
Hope someone can help:crazy:

I would like to know if a Electric installation Certificate for a new consumer unit can be use as an Electric Safety Certificate for a landlord?
 
I doubt it a FULL PIR would be required IMO but some of the guys will know better than me as Commercial doesnt realy come into landlord things
 
Thanks mogga
It seem`s a grey area, as a electrical installation certificate as every safety checks as a PIR
 
It all depends what is required, and what work has been carried out.
If a new installation has been carried out, then an EIC would be sufficient.
However, if or only an addition or alteration to an existing installation has been carried out, or no work at all, then a PIR/EICR will be required.
PIRs are what is usually refered to as Landlord Safety Certificates by laymen.
Ther is such a thing as a Visual Condition Report, something I believe the NICEIC have introduced.
Not something that I'd have anything to do with, but some people are happy with them.
 
Is there an editable template for the Visual Condition Report around (I have only seen on for the EICR)
 