sparkless
I suspect the OP is a D.I.whY
he should pay for a spark to install the shower and get off the forum
he should pay for a spark to install the shower and get off the forum
Why anyone would need a super mega watt electric shower, i still can't understand!! lol!! The 4.2 KW shower i'm using over here, delivers more than enough hot water for a good shower!!

Crikey!
I had to run a cooker circuit in 16mm in a bungalow once and that was horrific to terminate into the accessories
It was a big cooker and the calcs came to 16mm however i will admit that i forgot to apply diversity but the cable was buried in the wall then ran through 300mm of insulation in the loft then back down the wall

It was a big cooker and the calcs came to 16mm however i will admit that i forgot to apply diversity but the cable was buried in the wall then ran through 300mm of insulation in the loft then back down the wall
Forgetting to apply diversity to a cooker will always dictate a monster cable![]()
Regulation 510.3 is quite clear, even if you can prove via calculations that you can use a smaller cable, you must use the cable as given by the manufacturer!
'Every item of equipment shall be selected and erected as to allow compliance with the regulations in this chapter and relevant regulations in other parts of BS7671 AND SHALL TAKE ACCOUNT OF MANUFACTURES INSTRUCTIONS'.
If the manufacturer states you need a 10mm cable or whatever cable, then that's what needs to be installed!