Discuss Electrical Test sheets & Fudged Figures in the Commercial Electrical Advice area at ElectriciansForums.net
I need some advice, I've been doing the OM manuals for installations and come across an electrical test sheet which I believe is fudged.
Background of the story, is the handwritten one (NICEIC System was playing up) went walkies. Lost, never to be found. The QS produced the handwritten one, but didn't give me the opportunity to look at it and check whose handwriting it was. So week later I get a test sheet via email, with these figures on. Checked them out, ALL seemed completely fudged. The readings were too perfect. For a fact I know that building was tired, It wasn't a full strip out and installation. So you'd expect figures up and down.
What's the consequences of a fudged NICEIC certificate? (I've not issued it to the client yet)
I see you have no electrical experience, so you may not be able to answer my question, what readings are / where all to perfect? as to the consequences of a fudged certificate, if the only evidence you have is a bit hazy, it would be difficult to prove unless some sample tests were repeated, for comparison with the ones you have, you could report your thoughts to the QS and his boss, or the other option would be to contact the NICEIC, although there are some who think that is a waste of time, Can you scan the certificate and post a copy, erasing all the names of course.
I got someone who teaches electrical to check it over. Because I knew the original figures had gone missing and I was expecting this to turn up.
here's his reply
It looks fabricated- never in the real world do the values of R1 and R2 when added to the external value of Ze perfectly match the recorded value of Zs.
Sorry if that is technical but its simply the resistance of each circuit which then determines a number of safety features.
Yes its fudged
So on this job the ZE is 0.17
1 = 0.16 ZS = 0.33
2 = 0.19 ZS = 0.36
3 = 0.21 ZS = 0.38
5 = 0.23 ZS = 0.40
Also, My lads label up 1TP OR 4L1 So on so forth. But on this particular cert its just 1,2,3,4
Cheers
here's his reply
Yes its fudged
1 = 0.16 ZS = 0.33
2 = 0.19 ZS = 0.36
3 = 0.21 ZS = 0.38
5 = 0.23 ZS = 0.40
Cheers
I must admit they do all look like calculated results, are these the only results you are concerned over?
Do the values of Zs seem okay because I wouldn't lose sleep over some calculated continuity values. As for numbering the circuits there are no hard rules to this as long as they are clear.
Inspection and testing Guidance note 3
Earth fault loop impedance may be determined by
1 Measurement of R1+R2 and adding Ze
2 Direct measurement using a earth fault loop impedance tester
I may be barking up the wrong tree, and I agree with you on this, is it not bending the rules a bit as the results given are calculated readings of R1+R2 ergo R1+R2 = Ze+Zs at least I think that is what has been said
Well that may be the case Pete,however,the R1+R2 "is" a measured test and adding that to a measured Ze is whats allowed
There does not seem to be any compulsion to record a direct measurement, only that the reading is measured and step 1 is a measured reading
Agree Des but the readings (Fudged or not) indicate he has calculated R1+R2 by adding Ze to Zs that's all I was trying to say , crikey I'm even confusing myself:p
I'm looking at it the other way :)
The tester has measured and recorded R1+R2 and added it quite legitimately to the also measured Ze.
He comes up with a perfect Zs,whereas the op thinks that measured Zs is dodgy (because he thinks R1+R2 and adding Ze is a calculated reading)
I'm now getting flummoxed by what is being suggested
I think the op needs to expand on what he thinks is actually being fudged :)
I'm going for a lie down in a dark room
Reply to Electrical Test sheets & Fudged Figures in the Commercial Electrical Advice area at ElectriciansForums.net
Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit...
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Howdy folks, new member here. Homeowner, been doing my own electric for 40 years or so, from swapping out plugs to installing an entire circuit...
Hi everyone, A quick background to me and my question. I have been working for a commercial catering equipment engineering company for about 10...