- Reaction score
- 57
hi
i have a 60 amp main fuse supplying 63a main switch in cu. my question is about OSG table 1b max demand figures (calculations). When applying these figures ie no diversity for shower, no diversity for first ring main it seems that any installation with a 60a main fuse cannot have a electric shower as it is impossible for the calculated max demand to ever be below 60a. But how many 60a installations run perfectly normally with electric showers installed?
so i have a pre-existing 8.5kw shower currently installed in my own cu and depending on which method i use to calculate max demand it ranges from 95a(osg) to 54a. (40+30+30+30+5) x0.4 (rule of thumb)
now in using my own expieirience and kwowledge of how the installation is used i would bet that the max demand would be no more than 45-50a. With all loads switched on including shower/cooker/ringmain/lights clamp meter reading 57A
As this is for my elecsa assessment i wondered if i should dissconnect the shower circuit so that max demand as per osg table 1 can be met. Or leave as is and explain my reasoning