Discuss Exporting earth to another dwelling in the UK Electrical Forum area at ElectriciansForums.net

T

Tomm

Hi,

i Have been reading about exporting earths whilst surfing this forum on a quiet night shift. It seems to me that you can only export earth to an outbuilding if it doesn't have any extraneous conductors. So in theory I could supply a garage 20 m away in the garden and use the earth from the main dwelling for a two way board for sockets and lights only, but if I then decided to put in a water supply or run gas for a boiler I would then have to install an earth rod because I would then need to bond the incoming water and gas?
If I was to install an earth rod would you then get rid of the supply earth from the main dwelling and use the earth rod as your main earth? looking back on previous threads seems some people say you must use an earth rod, some say just use the armour of the swa and some say to run a 3 core swa as well as earthing the armour?

thanks
 
it's only when it's a pme earthing system that you need to bond any extraneous metal services with a 10mm bondibg conductor from the house MET. the SWA armour may be OK as cpc, but not adequate for bonding.
 
Extending the Equipotential zone to an out building with extraneous conductive parts is perfectly acceptable.
when selecting a cable to install to the outbuilding you will just have to also consider if the CSA of the cable meets at least the minimum requirements by bs7671 for bonding.


When using the steel armour of the swa for bonding you have to remember the resistivity of copper at 20C is 17.2 x10-9. The resistivity of steel varies with carbon content from 100 to 1000 x 10-9. GN8 suggests using a factor of 8 for the ratio of the resistivity of copper to steel.


For example if I calculated that the minimum sized cable needed was say 4mm due to volt drop, load, installation method, etc but I knew the outbuilding had extraneous conductive parts and I've looked in the book and know the minimum sized main bonding required was 10mm then I would select a 10mm 3core swa instead and use one of the cores as a combined CPC and main bonding conductor.


If you used 2core SWA and wanted to use the armour as combined CPC and main bonding conductor then due to using it for main bonding you have to remember the x8 rule for conductivity so if the minimum sized bonding had to be 10mm then due to the x8 rule the CSA of the steel armour would have to be 80mm
without looking I think the CSA of 70mm 2core xlpe swa is 80mm (I would have to check).


Another solution would be to use 2core SWA and run in a separate main bonding conductor to the extraneous conductive parts from the MET.
 
If your new incoming services are run in PVC then you don't have a problem!

Should you decide not to export the earth but to use an earth rod, then you'll need to install the garage wiring as a "TT".
 
The reason I ask is because I have just moved into a new house with a decent sized garage to the side of the house. It is supplied via a 6mm 3 core swa cable from the main house. It is on a 40a mcb in the house with a 40a rcd and a smal 3 way cu in the garage. We want to put hot water and a couple of radiators into the garage so I have Ben recommended a oil boiler to be placed outside the building. Reading through the regs and osg it seems to me that I will have to bond all copper pipe work entering the garage from outside. Because the earth supply to the house is only 6mm2 it seems I will have to install a bigger earth conductor from the house or install a earth rod. Please can you advise the way to go. The house is tncs

thanks
 
you could get round it by having any pipework entering the garage done in plastic.
 
The reason I ask is because I have just moved into a new house with a decent sized garage to the side of the house. It is supplied via a 6mm 3 core swa cable from the main house. It is on a 40a mcb in the house with a 40a rcd and a smal 3 way cu in the garage. We want to put hot water and a couple of radiators into the garage so I have Ben recommended a oil boiler to be placed outside the building. Reading through the regs and osg it seems to me that I will have to bond all copper pipe work entering the garage from outside. Because the earth supply to the house is only 6mm2 it seems I will have to install a bigger earth conductor from the house or install a earth rod. Please can you advise the way to go. The house is tncs

thanks

You could TT the garage end if you wanted to.

In comparison though would the cost of installing a bigger supply to the garage, a hot water cylinder with an immersion heater and a couple of panel heaters be cheaper than installing an oil boiler?
 
You could TT the garage end if you wanted to.

In comparison though would the cost of installing a bigger supply to the garage, a hot water cylinder with an immersion heater and a couple of panel heaters be cheaper than installing an oil boiler?

if I was to run a 16mm cable then I would also be able to use the earth from the house rather than install a ttsystem would I not? Need to price up the different options, I want to install something that I can expand in the future as the longer term plan is to convert it into a small bungalow. Won't be for a few years yet tho.
 
if I was to run a 16mm cable then I would also be able to use the earth from the house rather than install a ttsystem would I not? Need to price up the different options, I want to install something that I can expand in the future as the longer term plan is to convert it into a small bungalow. Won't be for a few years yet tho.
16mm it is then.

a tt is not as good as supliers earth


rule of thumb 16mm earth is around £1.70-2 a metre
 
Last edited:
if I was to run a 16mm cable then I would also be able to use the earth from the house rather than install a ttsystem would I not? Need to price up the different options, I want to install something that I can expand in the future as the longer term plan is to convert it into a small bungalow. Won't be for a few years yet tho.

Why 16mm?
 
Better off with a new supply from the DNO then!

But I still wonder why he thinks 16mm earth is required?

The bungalow will be for family it won't ever be sold separately from the house, So just as well be supplied from the house no additional meter or anything. Because I have 40m of 16mm 3 core in the store lol. Would you go 10mm or TT?
 
The bungalow will be for family it won't ever be sold separately from the house, So just as well be supplied from the house no additional meter or anything. Because I have 40m of 16mm 3 core in the store lol. Would you go 10mm or TT?

Good luck convincing the planning committee!

I don't know what I would use, there is not enough information! What is the Ib of the circuit, length, Ze etc etc?
 

Reply to Exporting earth to another dwelling in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
996
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
554
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
522
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock