I have a distribution cable to run for a domestic garage conversion - run length 40M - the main house is part of a PME system. There will be a fare loading on the new converted garage as it will have electric shower & heating. Is it feasable to export the earth from the PME or would it be best to have the garage conversion as a TT?
 
Hi and welcome to the forum.

Very long story short, TT the garage, especially as you have services going in there (water).

Also, you will need to install a fairly large cable to deal with the electric shower in there due to the loading and length of run and you also need to consider the route and if it would require RCD protection at the supply end. Obviously the garage CU will more than likely need it.

Depends on the installation method used.

Make sure you carry out all the calcs before you even begin the install.

Could be a very costly mistake if you undersize the supply cable.
 
Thanks for the pointers. I was planning to use 16mm twin SWA and TT the garage end. The route will be all external attached to a garden wall.:cool:
 
Hey Chloe

Just a thought. is your existing supply big enough to cope with the large additional load that you will be adding?? i.e DNO cut-out fuse and supply tails??
 
Just a pointer Chloe, but taking the sub main off before the CU won,t make any difference, you still only have a 100 amp incoming supply, and i think thats why lenny was saying about your max demand?
 

Reply to Exporting PME in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
484
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
6K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
847

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock