Thats TNC!!!
TNC-S Terra Neutral Combined (DNO!!!) Seperate (Consumer!!!)
Thats because the earth system is what it says in the name S - separate earth. As oppsosed to a combined Neutral and Earth conductor.
Do you actually understand the fundamentals of ''equal-potential bonding'' ??
Antimatter,
With the greatest of respect, you are 100% incorrect in this instance. Please examine the afforementioned literature and also contact your local DNO for further assurance if needs be.
There are probably hundreds of seperate threads on these forums regarding the exporting of a suppliers TN-C-S system and all conclude with the same answer which is, it's absolutely fine to do so providing any exposed steelwork/pipework that may be present in that building is connected to the installation M.E.T/B.E.M.T via a suitably sized main protective bonding conductor.
To continue in your current vane is non productive and misleading to others.
Regards.